    I am in the process of designing the electrical installation of a community centre, and have a question about the provision of three phase lighting for a large function room containing 18 36W LED fittings. All of the light fittings are to be switched simultaneously. Would it be possible to connect these lights in a three phase Delta configuration using 400V LED driver units, by connecting 6 light fittings/Drivers to each line, thereby ensuring a constant balanced load on each line? Presumably, I would not need to provide a neutral for each line, and could get away with just providing earthing for each fitting? Does anyone think that this design would be unsuitable?
     
  2. Vortigern
    Offline

    Vortigern Electrician's Arms

    Location:
    England
    Business Name:
    F.H. Electrical
    Why no neutral, surely the driver requires it. And why not put them on a single phase?
     
    • Agree Agree x 1
  3. Devonchris
    Offline

    Devonchris Regular EF Member

    Location:
    Devon
    Business Name:
    O
    My thoughts as well.
    Or, if the balance of the phases is that critical then a 3P contactor.
     
  4. snowhead
    Offline

    snowhead Trusted Advisor

    Location:
    Mildlands
    You're proposing 400v to the drivers, where are these to be mounted?
     
    • Agree Agree x 1
  5. telectrix
    Offline

    telectrix Scouser and Proud of It Trusted Advisor

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    for 650w of lighting, that's massive overkill. it's< 3A.
     
    • Agree Agree x 3
    • Funny Funny x 1
  6. Vortigern
    Offline

    Vortigern Electrician's Arms

    Location:
    England
    Business Name:
    F.H. Electrical
    By the way, what size is this function room?
     
  7. Vortigern
    Offline

    Vortigern Electrician's Arms

    Location:
    England
    Business Name:
    F.H. Electrical
    could be up to 1800A with inrush currents though or even more depending on the driver characteristics.
     
  8. westward10
    Offline

    westward10 In echoed steps I walk across an empty dream. Electrician's Arms

    Location:
    Northamptonshire
    Of course perfectly balanced single phase loads will function perfectly well without a neutral until something fails and then things don't function so well.
     
    • Agree Agree x 2
  9. westward10
    Offline

    westward10 In echoed steps I walk across an empty dream. Electrician's Arms

    Location:
    Northamptonshire
    Is this a wind up.
     
    • Like Like x 1
  10. Vortigern
    Offline

    Vortigern Electrician's Arms

    Location:
    England
    Business Name:
    F.H. Electrical
    Is that a wind up?:)
     
  11. Vortigern
    Offline

    Vortigern Electrician's Arms

    Location:
    England
    Business Name:
    F.H. Electrical
    Having looked at the content of previous posts..........Mhmmm
     
    • Dumb Dumb x 1
  12. westward10
    Offline

    westward10 In echoed steps I walk across an empty dream. Electrician's Arms

    Location:
    Northamptonshire
    No because three idential single phase loads will function on a three phase supply with no neutral. Bit yes thisvall seems like a wind up.
     
  13. telectrix
    Offline

    telectrix Scouser and Proud of It Trusted Advisor

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    how can a single phase load function without a neutral, unless it's 415V s.p.
     
    • Agree Agree x 1
  14. Vortigern
    Offline

    Vortigern Electrician's Arms

    Location:
    England
    Business Name:
    F.H. Electrical
    Ok because of the phase angle/voltage difference at each 120 degree angle but I can see that on say a single circuit like a water heater but separate circuits, that works? I can't quite think this out. Mmm maybe...why not indeed or even why
     
  15. telectrix
    Offline

    telectrix Scouser and Proud of It Trusted Advisor

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    the singlephase load requires 240V. the only way to get that from a 3 phase 415V supply is Ph -N, N being the star point.
     
    • Like Like x 1
  16. Lucien Nunes
    Offline

    Lucien Nunes Mercury Arc Rectifier Trusted Advisor

    Location:
    London
    If there is such a thing as a 400V LED driver, then yes. There's no need for a neutral and no need for loads to be balanced. Just connect them between any two lines and that's that. I'm not familiar with units that take 400V AC input though. And, uh, why?
     
    • Like Like x 1
  17. Vortigern
    Offline

    Vortigern Electrician's Arms

    Location:
    England
    Business Name:
    F.H. Electrical
    Well indeedy, why? Why not just the normal driver etc. What would the manufacturers say.
     
  18. telectrix
    Offline

    telectrix Scouser and Proud of It Trusted Advisor

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    they'd say you've put 400v across our 230V driver. warranty is void.
     
    • Funny Funny x 1
  19. westward10
    Offline

    westward10 In echoed steps I walk across an empty dream. Electrician's Arms

    Location:
    Northamptonshire
    Agreed but the star point requires no connection to neutral. I regularly used to demonstrate this by having three 60w lamps connected across three phases and the neutrals floating and just connected together.
     
  20. Vortigern
    Offline

    Vortigern Electrician's Arms

    Location:
    England
    Business Name:
    F.H. Electrical
    Sorcery!
     
    • Funny Funny x 2
  21. westward10
    Offline

    westward10 In echoed steps I walk across an empty dream. Electrician's Arms

    Location:
    Northamptonshire
    I think this hole thread is a fishing exercise from previous posts. It is not uncommon in large commercial or industrial installations to have three phase lighting circuits which incorporate a single neutral conductor provided you have a linked triple pole protective device.
     
  22. LankyWill
    Offline

    LankyWill Electrician's Arms

    Location:
    Northants
    Enlighten me fellas, how does it work without a neutral? i thought a neutral was required to create a potential difference thus allow the current to flow. Be gentle...
     
    • Like Like x 1
  23. static zap
    Offline

    static zap Regular EF Member

    Location:
    west midlands
    The whole basis of the three opposing phases is they always add to zero , making their own neutral when stared , saving on 3x Line currents flowing up return !

    Hence the preoccupation with balanced loads so neutral , doesnt get cooked up.
     
    • Like Like x 1
  24. AReynolds
    Offline

    AReynolds EF Member

    Location:
    United Kingdom
    Thanks for the replies, although I'm not sure why people are saying that this thread is an attempt at a 'wind up' or 'Fishing'- I am simply asking a question in good faith, as an electrician who has worked overwhelmingly in domestic installations and is trying to progress to commercial and industrial installations as well as design. Anyway, I realise that 400V, 3 Phase LED lighting is probably overkill in this case. Single Phase would indeed do the job well, if it wasn't for the length of the cable run, which would be about 50m from the Consumer Unit to the last light fitting, which may entail unacceptable voltage drop, and in turn require the use of 2.5 or 4mm conductors, which could be rather difficult to terminate in lighting accessories. As for the existence of 400V LED Drivers, they do exist (Although someone made a good point about them likely requiring neutral connection)- try Google if you don't believe me! Your responses have made me rethink the 400V three phase option- especially the fact that a malfunction of one or more of the lights could unbalance the loading of the circuit.
     
    • Like Like x 1
  25. static zap
    Offline

    static zap Regular EF Member

    Location:
    west midlands
    "cable run, which would be about 50m"
    Tighter specs on lighting volt drops ,doesn't help !
     
  26. marconi
    Offline

    marconi Regular EF Member

    'As for the existence of 400V LED Drivers, they do exist (Although someone made a good point about them likely requiring neutral connection)- try Google if you don't believe me! '

    Out of curiosity I did a google search and found this example:

    LPFH-60-54 - MEAN WELL - TRC Electronics - http://www.trcelectronics.com/View/Mean-Well/LPFH-60-54.shtml

    I note though that the input voltage specification is 200 - 400V ac to 'Meet 277Vac and 347Vac input requirements of North America'. At first glance then, the manufacturer has in mind two operating voltages lower than the upper figure of 400V. The three phase supply in my road in London is 242 x square root of 3 = 420V.
     
  27. Andy-1960
    Offline

    Andy-1960 Electrician's Arms

    Location:
    Wolverhampton
    As was stated earlier, if you are planning to switch them all on at the same time, beware of the inrush current, as this may cause nuisance tripping of the protective device. I recently looked at some 140w led fittings .. inrush current was 10.2A per fitting!
     
  28. Vortigern
    Offline

    Vortigern Electrician's Arms

    Location:
    England
    Business Name:
    F.H. Electrical
    Think water heater 3 phase, or motor. P.D. between the phase angles. So Phase 1 peaks, phase 2 rising P.D. between the two etc. Ph. 3 as well. Thats how I (mis?)understand it.
     
    • Useful Useful x 1
  29. westward10
    Offline

    westward10 In echoed steps I walk across an empty dream. Electrician's Arms

    Location:
    Northamptonshire
    No you nailed it in #20, sorcery.
     
    • Funny Funny x 1
  30. Vortigern
    Offline

    Vortigern Electrician's Arms

    Location:
    England
    Business Name:
    F.H. Electrical
    I don't know quite why, but every time I get an alert from @westward10@westward10 I get worried.
     
    • Funny Funny x 3
  31. Lucien Nunes
    Offline

    Lucien Nunes Mercury Arc Rectifier Trusted Advisor

    Location:
    London
    This works in star with a floating star point using filament lamps, because the loads, despite their large temperature coefficient, are approximately resistive for a small change in temperature, and at least are always electrically continuous. Electronic drivers are switched-mode power supplies that work at approximately constant power input so they can have negative dynamic resistance, i.e. the current falls as the voltage rises. A unit that, through minor differences in load or construction tolerance, is using slightly less current, will receive slightly higher voltage just as though they were in series on a single pahse supply. This will further reduce the current and the system will experience positive feedback, almost inevitably swinging to extreme unbalance until one unit receives too low a voltage and shuts down. At that time almost the full 400V will be across the unit that is still operating, until it decides not to operate any more! The same will occur if one unit starts up slightly quicker than another.

    In summary - identical single-phase loads in star with floating star point, OK with constant resistance loads like heating elements, no good with electronic loads even if apparently perfectly balanced.
     
    • Agree Agree x 2
    • Like Like x 1
    • Useful Useful x 1
  32. westward10
    Offline

    westward10 In echoed steps I walk across an empty dream. Electrician's Arms

    Location:
    Northamptonshire
    Agree and it would be foolhardy to install any lighting circuits across a three phase supply with no neutral.
     
  33. HandySparks
    Offline

    HandySparks Trusted Advisor

    Location:
    Hampshire
    Business Name:
    Neish Electrical Services
    So make the main run in 4mm², or whatever, then into a junction box and drop down to 1mm² or 1.5mm² for the final link to the fittings.
     
    • Like Like x 1
    • Agree Agree x 1
  34. HandySparks
    Offline

    HandySparks Trusted Advisor

    Location:
    Hampshire
    Business Name:
    Neish Electrical Services
    So make the main run in 4mm², or whatever, then into a junction box and drop down to 1mm² or 1.5mm² for the final link to the fittings.
     
  35. davesparks
    Offline

    davesparks Trusted Advisor

    Location:
    guildford
    In star yes, but he's talking about delta, balancing of the loads won't be necessary.
     
  36. Vortigern
    Offline

    Vortigern Electrician's Arms

    Location:
    England
    Business Name:
    F.H. Electrical
    You know @westward10@westward10 that sorcery you do with the lights you ought to set up a rig and demonstrate that here on the forum. It would be great to demonstrate graphically to all the theory of circuits and 3 phase etc. Of course you would have to warn us not to do it at home.
     
    • Like Like x 1
  37. westward10
    Offline

    westward10 In echoed steps I walk across an empty dream. Electrician's Arms

    Location:
    Northamptonshire
    It will work in star with three tungsten lamps.
     
  38. davesparks
    Offline

    davesparks Trusted Advisor

    Location:
    guildford
    It would be an unconventional, and in my opinion design which will lead to maintanence issues in the future as the drivers will be non-standard and hard to replace. You will also be putting 400V where nobody normally expects to find it.
    You'll also need the neutral anyway as you almost certainly won't get emergency lighting that'll work on 400V.


    2.5mm is pretty common as a minimum size of conductor for lighting circuits in commercial jobs. It's not too bad to terminate into the usual fittings (rock rose etc) if you're careful.

    Have you actually calculated the voltage drop or are you just guessing?
    Even if you were daft enough to put the whole lot on to one single phase circuit a quick calculation suggests that 1.5mm would be fine if you connected the whole load at the very end of a 60m cable run. So in a real world scenario where the load would be distributed along the length of the circuit, and you'd almost certainly spread them across at least two circuits for a bit of redundancy should one circuit trip, I can't see any issue.
     
    • Agree Agree x 2
  39. marconi
    Offline

    marconi Regular EF Member

    (Posh) Wet pants explains 3 phase electricity. Enjoy

     
  40. Matthewd29
    Offline

    Matthewd29 Regular EF Member

    Location:
    Belfast
    Surely the driver has to have a neutral?
     