Hi guys so found out my house has no bonding today so am straight on it and getting that done tomorrow and getting my incoming water bonded, but i do have a question regarding my boiler/radiators, i have oil from outside come into my boiler to do the heating and hot water.
The boiler is on a fused spur on its own circuit. So my question is would i need to bond the oil pipe as it comes in or is it ok seeing as the boiler has its own earth path and all the circuits are protected by RCD, which would make it supplementary bonding which isnt needed as the main bonding is in place and because of the rcd?

Cheers guys
 
If the oil pipe comes in from outside and outside goes underground or is connected to a metal oil tank firmly attached to the ground then it is very likely to be an extraneous conductive part. In some cases the oil pipe is not accessible but often the connection to the boiler continues the conductivity to an accessible place.
Therefore subject to appropriate testing of the resistance to earth of the oil pipe it is likely that this would need to be bonded back to the MET.
 
I actually got into a discussion about this in the week when we had our oil boiler serviced. The service chap asked me if the oil service should be bonded because mine is not and started talking along the lines of what Richard states. I got blank looks and apparently is is an OFTEC requirement that it should be bonded regardless, every year he crosses this as a departure.
 

Reply to Question regarding bonding in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Curious about supplementary bonding, I have these two 4mm Cables loose and not connected to anything in my parents house. I presume they are for...
Replies
9
Views
2K
So was on a call out today and cooker circuit kept tripping the RCD. Disconnected at the board and at the cooker switch and IR’d the cable and...
Replies
9
Views
357
Hi, I'm having a new boiler fitted in a new location. I need to provide power for the boiler which I'm looking to do myself. Boiler: Ideal Logic...
Replies
11
Views
2K
evening everyone . Quick question here I’ve recently took over a job that a friend of mine first fixed it’s a 3 bed semi house rewire. I don’t...
Replies
10
Views
1K
Legends, need some advice. I am a 12v automotive electrician, but have had a side project building a concession trailer for my dad. We have an...
Replies
6
Views
713

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock