nazoom

Can we carry out the continuity test for the ring final by connecting the line, neutral, and cpc end to end at any socket or do we have to identify and disconnect the conductors at the C/U? I am aksing as i think it is much easier to link the line, neutral, and cpc end to end at any socket rather than C/U.

Many thanks
 
You could, but can you confirm that the end to end measurements are of the RFC and not parallel paths/interconnections from other circuits?

Tend to find a bit more cable in the CU to work with as well.
 
You could, but can you confirm that the end to end measurements are of the RFC and not parallel paths/interconnections from other circuits?

Tend to find a bit more cable in the CU to work with as well.
Not sure I understand what you mean there Strima?

It's easier to identify ends at a socket than the CU (unless it's a beautiful CU you've just installed yourself of course) and you can be pretty darn sure it's the correct ring.
 
Well I'm going to myself now never thought of doing it at socket great idea the times I've struggled getting cables out of board specially when there full of rcbos in a 3 phase board great site this always learning new things
 
If there is some parallel path, e.g. due to CPC bonding somewhere, if you don't disconnect the parallel path, you could obviously end up with too low a CPC end-to-end measurement. Since the CPC connection at the CU / MET is likely to be one end of such a parallel path, not measuring at the CU is perhaps more prone to such an error?
 
biff 55 how could you take a test for any one . with a face loike that i think that you would stick out like a sore thumb
unless nazoom looks like you
 

Reply to Question regarding Continuity of Ring Final circuit. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi All Happy new year to all! First post but long timer lurker, so thanks for all the previous help! Just wanted to clarify something I have...
Replies
7
Views
823
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi. I'm in the process of getting my qualifications and am taking on some small jobs for family to try and get some experience in. Today I was...
Replies
17
Views
796
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
796
I have got these questions on 2391-52 inspection and testing but can't remember option of 1st two questions. Please any suggestion will be...
Replies
2
Views
650

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock