All,

I have a 2.3Kw single oven. My current wiring is 10mm over a 10m run to cooker switch, 6mm to dual ccu and my plan is to wire both hob and oven directly into this in 4mm. The oven manual states fuse must be minimum 13amps. I just want to double check that the 45a cooker switch is ok since it's a lot higher? Hob is 5.8Kw with min 23a fuse.
 
Last edited:
the oven can be classed as a fixed load, therefore there is no need for overload protection, only s/c protection, so wired direct from the CCU is fine. you could, if you wanted to feed oven from a 13A FCU from the 45A isolator, but it;s not necessary.
 

Reply to Quick oven question in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hello hope you can help I have a single oven 2.4kw max and a ceramic hob 6kw max I would like to put then both on the same circuit so i was...
Replies
0
Views
1K
(Trying again, as picture didn't post first time) Hi, I'd be very grateful if anyone could help me here. Below, I've pasted a sketch showing how...
Replies
5
Views
1K
Hello everyone, I'd like to seek your input on a matter. I'm in the process of designing the electrical connections for the following kitchen...
Replies
38
Views
3K
I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
789
Hi all Some advice on this would be great. Due to wire a kitchen from scratch and in a pickle over the designing of the oven and hob circuits due...
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock