Hi all.

I am looking to fit a couple of blue 230V single phase 32A sockets for a portable welder in a workshop. Indoors. Though the welder has the option to be outdoors on a long flex. Two sockets as it gets wheeled around and used in two locations and the current long extension flex gets in the way.

Questions:

1) Do the sockets need to be on their own radial circuit? (I'm assuming so as the potential for them pulling close to 32A is high, the welder is rated 25A)
2) Is there a reg that says they have to be the switched 'interlock' sort of socket, or just normal angled sockets with a flap?
3) Run off a phase from the 3ph panel through a 30mA 100A RCD and 32A MCB, or ...just a 32A MCBO??? I presume it should have an RCD even though it's a 32A socket?

Many thanks in advance.
 
Ideally they should be on their own 32A protective device with 30ma additional rcd protection. There is no requirements for an interlocked switch although this can help preserve contact surfaces to prevent a plug being inserted under load.
 
If you only have the one welder, then a single radial will suffice.
You could possibly get away without providing RCD protection if you produce a Risk Assessment that concludes RCD protection is not required.
 
If you put them on the same radial it may be difficult to terminate 2 cables in the same terminal also I use Interlock sockets as there is normally more room to terminate the cables in . But as westward said I don't know any reg that states you have to use Interlock ones unless the manufacturer instructions of the welder requires it.
 
Certain regulatinons for their use would come into play depending on the environment and the associated risks that could arise from non interlock sockets being used
 

Reply to Quick Question(s) - BS4343 Sockets - switched/interlocked or not? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Replies
3
Views
2K
Hi all, Just to be clear, I'm not looking for advice on upgrading but rather just clarification of our existing setup. We need to upgrade the...
Replies
12
Views
1K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
Hi all, Newly qualified electrician here who is in the process of re-wiring my own property. I have recently converted my old CU (if I can call...
Replies
10
Views
2K
My wife is on the committee of the local village, and they have just had an EICR carried out. This came out as 'unsatisfactory' and accompanied by...
Replies
14
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock