R1+R2 on a cooker circuit with a combined 13a socket is it ok to plug into socket and test between R1+R2 on plug in socket to get reading for cooker, I say yes but who I'm working with says face plate needs to come off
Discuss R1+R2 on a cooker circuit in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Test at the low level outlet that you connect the cooker toR1+R2 on a cooker circuit with a combined 13a socket is it ok to plug into socket and test between R1+R2 on plug in socket to get reading for cooker, I say yes but who I'm working with says face plate needs to come off
I'd take the face plate off because although your not testing at the outlet if it's inaccessible I'd do it so you can confirm at least polarity leaving the control switch to the outlet if that makes senseIt's an intergrated appliance so cooker outlet on wall only place to go
I meant the cable leaving the control unit to the outlet you can visually inspect polarity leaving the switch. It's better than nothing in my view even tho it maybe be a limitation on the eicr^^ if the socket is integral to the cooker isolator, then the polarity will be confirmed at the socket
That way you are proving the earth continuity which is most of all the safety element & polarity up to the point of cooker switch.Yup that's my route. Live at the socket CPC at the cooker. Make an assessment of the cable length and CSA and use that to ensure R1+R2 is compliant.
That way you are proving the earth continuity which is most of all the safety element & polarity up to the point of cooker switch.
The word your looking for is limitationYes. I'd visually check the back of the cooker switch to check the cabling is correct and secure. The only variable then is the other end of the cable that connects to the cooker. And if its built in that's the too hard department.