    Hi All, quick question before bed.
    Just come back from an emergency callout


    1. No Earth in property
    2. 6 double sockets on a 15A Radial (over 2 floors)
    3. 3036 CU with big hole out of R/H side
    4. Bonding to mains Water - 16ohms through this means
    5. No Bonding to Gas
    6. Pre RCD covering 4 x 3036 CUs
    7. Pe-RCD not holding on circuit 6 (point 2) - all appliances are class 2
    8. All IRs are >150Mohms

    Full installation isolated - customer re-energized when I walked out of the door due to medical conditions

    Thoughts please with particular attention to point 2! - will pick this up in the morning
     
  2. GLENNSPARK
    Offline

    GLENNSPARK Electrician's Arms

    Location:
    west yorks.
    start isolating each board...till you find the offender...

    then narrow it down to the final on that board...
    there...identified the circuit/s causing it....and that without any test gear...

    it could of course also be a case of accumilated leakage....
     
  3. LED Lighting
    Offline

    LED Lighting Regular EF Member

    Location:
    Wales
    Like i said found the issue in circuit 6, well customer did before I got there.
    all irs are good on everything.

    the RCD only trips after about 1 min of circuit 6 being turned on, all appliances plugged in are class 2.
    no tripping when nothing plugged in

    this is the same circuit that had 6 double sockets on a radial

    i have put it in for remedial work so just a wait and see now - out of my hands
     
  4. GLENNSPARK
    Offline

    GLENNSPARK Electrician's Arms

    Location:
    west yorks.
    so..its a neutral earth fault then...isn`t it...
     
  5. LED Lighting
    Offline

    LED Lighting Regular EF Member

    Location:
    Wales
    Not sure as all IRs are good and with everything connected but circuit 6 isolated at MCB the RCD held for over 30mins

    could lack of earth cause this? Or the high load on circuit 6???
     
  6. GLENNSPARK
    Offline

    GLENNSPARK Electrician's Arms

    Location:
    west yorks.
    eh?..
    whats this got to do with RCDS?
     
  7. GLENNSPARK
    Offline

    GLENNSPARK Electrician's Arms

    Location:
    west yorks.
    get a leakage clamp on this...

    if you dont have one then ramp the RCD off load...then ramp it again with everything on...the difference is leakage...
     
    • Like Like x 6
  8. HandySparks
    Offline

    HandySparks Forum Mentor

    Location:
    Hampshire
    Business Name:
    Neish Electrical Services
    No and no.

    And there's nothing unsafe about 6 double sockets on a 15A radial, provided that the current rating of the cable is suitable. The worst that's going to happen is the fuse blowing on overload and having to be rewired.
     
  9. LED Lighting
    Offline

    LED Lighting Regular EF Member

    Location:
    Wales
    Thanks all

    I work for British gas home assist, and this was one of the call outs last night

    i have put the work forward now to be done, and will await their response.

    circuit 6 has 2.5mm T&E off a 15A radial. I know its safe as fuse is less than CCC of cable, but was not sure if circuit is being overloaded.

    thanks for the advise on leakage, I am trying to get myself a clamp, any recommendations?
     
  10. LED Lighting
    Offline

    LED Lighting Regular EF Member

    Location:
    Wales
    Im still lost with regards to how this circuit can leak current when IR is >150Mohm with items plugged in and not (N/E).
    Also all items plugged into this circuit are class 2 so there cant be any leakage there????????
     
  11. ifindoubtdont
    Offline

    ifindoubtdont DIY

    If it holds with nothing plugged in and pops when something is plugged in and switched on, accessory fault. If it pops when just plugged in, accessory fault and polarity issue at socket (has customer been fiddling before you arrived). Is there an immersion heater or something similar on this circuit.
     
  12. LED Lighting
    Offline

    LED Lighting Regular EF Member

    Location:
    Wales
    no Immersion Heater or anything like this
    From my memory:
    • 2 house phone chargers (class 2)
    • oxygen machine (class 2)
    • 3 bedside lamps (class 2)
    • 2 floor lamps (class 2)

    IH on its own circuit - IRs over 500Mohm with on and off

    What got me was it would hold for 1 min but then trip, but first time I turned it back on after main IR Testing, it held for around 30mins then tripped - everything plugged in at this stage and turned on

    only thing I can think of is slightly warming the cables and POP
     
  13. Badged01
    Offline

    Badged01 DIY

    Location:
    Portugal
    You're never to old to live'n'learn on this forum! Ive always used a clamp meter and hadn't even thought about using the RCD on ramp, thats one up my sleeve for the time my clamp runs out of battery power .....
     
    • Like Like x 3
  14. Murdoch
    Offline

    Murdoch Regular EF Member

    Location:
    Woking
    Is it me but if its a 3036 board where are the RCD's? am I being dim?
     
  15. LED Lighting
    Offline

    LED Lighting Regular EF Member

    Location:
    Wales
    Pre RCD (General RCD covering whole installation - all CUs)
     
Loading...
Similar Threads - Radial Circuits Forum Date
Can I use a 32 amp rcbo on a radial circuit. Electrical Wiring, Theories and Regulations Monday at 7:04 PM
4mm t&e radial circuit Electrical Forum Friday at 5:55 PM
Thread Status:
Not open for further replies.

Share This Page

Electricians Directory Post a Domestic Job Post a Commercial Job