    Hello all, first time posting here, was hoping for some theories/advice regarding a confusing situation. Essentially we were looking to add one or two sockets to a upstairs bedroom (40's build rewired in 80's I think with black/red colour system). It currently has two sockets and there is also one in the landing which according to the consumer unit is all wired radially of a separate fuse on the unit. Downstairs is on a ring main and there is another radial route for front two bedrooms from the consumer unit on a different fuse.

    Now, my confusion comes because when trying to isolate this circuit, the sockets remained live on testing even with the proper fuse removed. I have since determined that if the lighting circuit MCB is also off, then these sockets are dead. However if EITHER the lighting fuse OR the radial fuse is on, these three sockets receive power. Any ideas what may be going on before I pull up the all the floorboards?

    Additionally, this is an old consumer unit we are getting replaced as it doesn't have RCD protection and runs of the old 2 pin fuses but this will probably throw up testing problems afterwards if somehow the lighting circuit and this radial spur are connected somewhere

    Many thanks
     
    Last edited: May 17, 2018
  2. Pete999
    Offline

    Pete999 Forum Mentor

    Location:
    Northampton
    Business Name:
    None
    Mate you seem to be getting MCBs RCDs and fuses mixed up, which in turn makes your post difficult to understand, is there any chance you could post a picture of your Consumers Unit (fuse box), it would go a long way to helping people decypher what exactly you have as far as electrical distribution in your house, please get back as soon as you can.
     
  3. Szico VII
    Offline

    Szico VII EF Member

    Location:
    UK
    Sure please see below.

    TLDR: Sockets in one room and landing seem to operate with either lighting or the specific fuse for the radial upstairs circuit on at the control board. (And the control board doesnt have RCD protected fuses)

    Edited original post for clarity as well

    20180517_134540.jpg
     
  4. Szico VII
    Offline

    Szico VII EF Member

    Location:
    UK
    Here are the three sockets which appear to be live when either the lighting MCB OR the radial fuse are on/live.

    It seems the last socket is the one in the 2nd image (134933) as that only has one wire going to it.

    20180517_134926.jpg

    20180517_134933.jpg

    20180517_134950.jpg
     
  5. Murdoch
    Offline

    Murdoch Regular EF Member

    Location:
    Woking
    My best advice is to get a competent spark involved ....
     
    • Agree Agree x 3
    • Like Like x 1
  6. Pete999
    Offline

    Pete999 Forum Mentor

    Location:
    Northampton
    Business Name:
    None
    You need to employ an Electrician mate to sort this out, obviously somewhere inside your CU someone hs botched up the circuitry.
     
    • Like Like x 1
  7. Andy78
    Offline

    Andy78 Respected Member

    Location:
    Kingston upon Hull
    As above, a local reputable electrician should be your next call.
     
  8. Szico VII
    Offline

    Szico VII EF Member

    Location:
    UK
    The electrician is already booked and coming to change the consumer unit next Thursday and obviously has to test the whole system afterwards, I have given him a heads up about this new finding but was curious as to what people thought the likely cause was sounds like mis-wired consumer unit most likely then?
     
    • Agree Agree x 2
  9. SJD
    Online

    SJD Forum Mentor

    Location:
    Braccan heal
    Curiously enough, I came across a vaguely similar type problem a couple of weeks ago. A security light, powered by both the lighting circuit and socket circuit - so it came on either with a light switch or the PIR sensor operating.

    Net result, when light switch is on and PIR operates, then a socket ring final circuit and a lighting radial circuit became cross connected. The previous owner had somewhat helpfully put a note in the fuse box lids "to isolate both circuits when working on this light"!

    I'm not suggesting this will be your problem, but that someone somewhere has done something stupid and dangerous because they didn't understand the implications.
     
    • Like Like x 1
  10. DPG
    Online

    DPG Respected Member

    Location:
    S Yorkshire
    Please let us know the outcome - sounds interesting!
     
  11. Szico VII
    Offline

    Szico VII EF Member

    Location:
    UK
    Will do, in the meantime gonna get all the backboxes in and wiring (not live) then connect it up once the root issue fixed
     
  12. Murdoch
    Offline

    Murdoch Regular EF Member

    Location:
    Woking
    I did a board change a while back ................. some muppet had connected the immersion circuit AND the upstairs lighting together ...... very odd thing to do
     
    • Like Like x 1
  13. johnduffell
    Offline

    johnduffell Regular EF Member

    Location:
    uk
    The is a connection between the live conductors of the two circuits. This could be in the cu, in an accessory or other termination, or due to failed insulation somewhere.
    Only a fault finding procedure including testing and inspection of the circuits would determine where the issue is.
     
  14. pirate
    Offline

    pirate Regular EF Member

    Location:
    Glasgow
    40's build you say? That door looks 30's to me, but maybe they just carried over? Whatever, preserve those doors! and handles! Period, they are!
     
  15. Adam W
    Offline

    Adam W Regular EF Member

    Location:
    Bournemouth
    I'd be surprised if that was intentional. It's the uninitiated person's approach to electrics - if something doesn't work then turn things on and connect things together until it either works or goes bang.
    Chances are in this instance they were content that the lights came on and left it at that before they stopped working again, or went bang; a partial victory.
     