adamsnell

Hi,

We have a Rafiki Twinflex 8 Zone Control Panel in our residential building which is showing an orange fault light and beeping continuously. Can anyone recommend what the issue might be?

See attached a photo of the control panel.

Thanks.
 

Attachments

  • Rafiki.jpg
    75.4 KB · Views: 33
Zone 4 & fault indicates o/c or s/c on the zone. Before you do anything, these panels are trouble. So suggest doing a processor reset just to make sure. On the main pcb press the reset button...and wait till panel reconfigures. The press ACCESS / 514 / RESET SYSTEM. Hopefully all will be ok, if not then time to check detection leds for status.
 

Reply to Rafiki Twinflex 8 Zone Control Panel - Fault in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K
Hi all, Wondering if you could offer some advice please. I carried out a small outdoor lighting project today at a commercial property. 4 lights...
Replies
5
Views
868
Hi all, total newbie to the forum. I sincerely hope that those in the know-how would be able to assist me. On my semi-detached house we have an...
Replies
13
Views
2K
Hi, I would love some help understanding an issue I’m having on a 16mm SWA cable running from the CU in my house to the CU in the shed. I believe...
Replies
15
Views
2K
Good afternoon all, Our company installs fire alarm systems in convenience stores but it's always limited to a conventional system whether it be...
Replies
4
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock