Hi guys
First post so go easy on me!!

Im trying to put an RCBO into an old MK board. I am gonna double up the lighting as its all on LED bulbs and use the space to add a 40A RCBO which is powering a 2 way in the shed. Now im not sure if i can use the modern RCBO's in this board.

Ive seen this one Space does not seem a problem:

MK Sentry 6937S Single Module RCBO, 40A, 30Ma | eBay - http://www.ebay.co.uk/itm/MK-Sentry-6937S-Single-Module-RCBO-40A-30Ma-/201683672920?hash=item2ef5489f58:g:BtcAAOSwMgdXwu6Q

Ive attached a pic of the board

IMG_3195.JPG
 
if you're using SWA to feed the shed, why not RCD at the shed? and i hate spaghetti.
 
New rcbo will fit but I agree with Tel fit rcd at shed. Me personally would not double up circuits, nasty practice. I would suggest upgrading the CU.
 
If you double up the lights and are later asked to do a EICR it won't look very good.
What about the new ring main with no RCD protection. With price of MK rcbos looks like a new board to me.
 
It's just an old house. That's what they did in our day. I'm surprised to see the MCBs; very modern!!

The sentry range will be too long but the Hager range of MCBs will fit the old MK boards. Worth a try.

Cheers

Ken
 
It's just an old house. That's what they did in our day. I'm surprised to see the MCBs; very modern!!

The sentry range will be too long but the Hager range of MCBs will fit the old MK boards. Worth a try.

Cheers

Ken
What do you mean that is what they did in our day, the old MEM board looks original but the rest isn't. So we are going from doubling up circuits to fitting non compatible devices. Is it just me ?
 
Sorry! I was trying to be funny; obviously not.

When It is not practical or economic to rewire the whole house (I'm exaggerating) and a simple solution solves the problem and doesn't break the regulations, then it is justifiable.
 

Reply to RCBO for old MK board in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I had a call to a new customer who was experiencing what sounded like nuisance tripping on a kitchen ring. Some background first. It's an MK LN...
Replies
4
Views
708
I need to fit some RCBO's into this board. I realise they don't fit in place of the LN range but these don't say LN on them and it doesn't look...
Replies
11
Views
4K
I need to get 30mA RCD protection to a new circuit I am putting on this consumer unit. I didn't take the cover off so I am not sure if there will...
Replies
7
Views
2K
....To fit old Sentry board. Present board has 80A, 30mA RCD mainswitch, and it’s a 16 way board!! I can’t get all circuits to stay on all at...
Replies
19
Views
5K
Hi guys, Been asked to run a circuit for a hot tub the board is an MK Sentry (the old one with the plastic cover) but all of the RCBOs fitted in...
Replies
4
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock