Just wondering if I'm thinking correctly here....

Newley installed rcbo, but not tripping when tested at x1 and x5 ?

Got to be either a dodgy rcbo unit (was a cheaper make - CED) or maybe a dodgy earth connection ?

Many thanks,

Sy
 
Yep tester all good, leads good, 30ma set all ok.... not tried another rcbo yet. But if it's not that I'm thinking it's got to be earth prob?
 
i had the same problem with the RCBO not tripping and although i got a reasonable r1r2 resault it all came down to a loose earth connection so i think your instincts may be right
 
ZS will clarify any earthing problem.
Also was meter on G setting and not time delay?
Heard a couple of years ago a load came over with nothing inside from China.

Paul
 
Sorry chaps... delayed reply there, only a day late !! Lost my www connection for a while, then fell asleep.

It ended up being dodgy earth connection, thanks for all your help and advice..

Much appreciated,

Sy
 
Sorry chaps... delayed reply there, only a day late !! Lost my www connection for a while, then fell asleep.

It ended up being dodgy earth connection, thanks for all your help and advice..

Much appreciated,

Sy

Before you test any RCD you need to confirm like the guys have said you have a good Ze your gas & water earths are connected then do yor circuit Zs then at the end do your RCD test
 

Reply to RCBO not tripping on x1 and x5 tests... thoughts please....? in the Australia area at ElectriciansForums.net

Similar Threads

Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
290
I will start with apologies, as I have not thought this through very much (at all) yet and have just sat down with a beer.... meaning I thought...
Replies
3
Views
1K
Hi all. Have an issue i'd love some advice on if anyone would be so kind. Will try to be brief. Thank you!! So, have an intermittent RCD trip at...
Replies
43
Views
3K
Hi Have a nightly problem - will be changing a consumer unit however have a problem customer has an older mem m6 32amp rcd/mcb on downstairs ring...
Replies
10
Views
4K
Hi all, Im new to the forum and wanted to check something and maybe get some advice confirmation. Ive got halogen wall lights which use a...
Replies
6
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock