Mr.B

Hi

I just wanted to clarify some things that i have been told by my maintenance contractor.

I am in a large commercial building and we have a terrace which had 8 bulkhead lights. We wanted these changed as they where getting old and grotty and now we have some nice feature lighting. I was told the install does not need a RCBO as it is looked after by a 'skilled or trained person' and also that it is wired in armoured cable.

The building has only been refurbished 2 years ago and did not have a rcbo fitted then so i have taken there work for this, but i do have some slight doubts and was hoping somebody here could help me with this.

Regards

Pete
 
Your Electrical maintenance contractor is quite correct and there is no need for there to be protection by RCBO. IMO I would give you what you asked in the regard, unless fitting the RCBO was really prohibitive, and if asked for a RCBO protection then that is what you would get, and cost accordlingly.
 
I was really just backing up what my boss had got me to check out i have a general knowledge of things but not to in depth.

Is there any regulation numbers that i can quote? I do have a copy of the regs and if maybe somebody could explain to me why it does not need a rcbo. Rather have all the details now then have to keep coming back.

Regards

Pete
 
The regs wouldn't specify why something is not required,rather what requires additional protection by rcd

559.10.3.2 will tell you where lighting systems are recomended to have rcd additional protection,then as long as the rcd is not required for buried cables.TT system etc
If it doesn't come under a requirement thats the difinitive answer
 

Reply to RCBO Outisde Lighting in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi All I'm new here. I have just finished my NVQ and waiting to do my AM2. I have a question on selectivity as it has always slightly confused me...
Replies
5
Views
731
Hi all, Wondering if you could offer some advice please. I carried out a small outdoor lighting project today at a commercial property. 4 lights...
Replies
5
Views
852
Hi all Now being upfront I am not a sparks. I am about to have some work done by a friend (certified) and as he is doing me a favour I want to as...
Replies
5
Views
1K
I had a PV system installed by a local reputable manufacturer last autumn; since then, I've received conflicting advice regarding the consumer...
Replies
2
Views
2K
Hi, I've just had some electrical work completed in the bathroom; I've recently refurbished the bathroom, replacing the old electric shower with...
Replies
39
Views
8K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock