Discuss RCBO - What would happen if I didn’t connect the neutral of the RCBO? in the UK Electrical Forum area at ElectriciansForums.net

Ok thanks , someone told me the neutral fly lead of the RCBO didn’t have to be connected thought it was rubbish
Tell that person they are an idiot !

An RCD monitors the current flowing in both the line and the neutral, and when there is an imbalance between the two, the RCD trips. The functional earth fly lead is required to be connected to earth so that the test facility will work. All an RCBO is, is an RCD combined with a CB
 
if you don't connect the neutral, the circuit will not work.
 

Reply to RCBO - What would happen if I didn’t connect the neutral of the RCBO? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I’m probably going to look stupid here, but it will be worth it if I get the answer 😆, as I can’t fathom it out. I’ve never really thought of it...
Replies
22
Views
681
Hi all, Wondering if you could offer some advice please. I carried out a small outdoor lighting project today at a commercial property. 4 lights...
Replies
5
Views
858
Hi, I have just replaced an old rewireable fuseboard with a 10way consumer unit with rcbo's fitted. The issue i have is that when i connect one of...
Replies
19
Views
2K
Hi Guys, Had a call out today about an odd issue with a newish Creda DT storage heater. Basically.. Storage heaters were installed in one flat...
Replies
4
Views
755
So I had an inquiry to make an electric panel (single phase) with RCBO, but it seems like our customer uses type C and F power plug (I live in...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock