I've used a particular socket in my kitchen to carry out monthly calibration checks (ZS & RCD) on my MFT, for several months with no issues. Last week I carried out my tests on my MFT and the x5 RCD test timed out at 40ms. Thinking I had a faulty RCBO, I replaced today, but the fault remained. Disconnected all loads & appliances, carried ou R1, Rn & R2 tests, insulation restance test & ZS. All good, so decided to carry out auto rcd rest after pluging back each appliance, and the washing machine stops the RCBO tripping at x5. Not PAT tested trained, I suspect some earth>live>neutral fault, but can someone explain why the fault would stop the RCBO tripping at x5:confused:
 
Strange, I know some white goods can 'leak' some earth leakage and function perfectly without tripping an RCD --- i.e. the leakage is below 30mA. I would have thought that if the washer was 'leaking' a little (or its an accumalation of leakage from all you have plugged in) then the RCD test would actually trip earlier and your time would be quicker?
 
Nope, tried it a couple of times and it caused the rcbo not to trip @ x5. I've experienced a neutral to earth fault before on a cable that stopped an RCD from completely working!

The washing machine is built in. So its turned off till I can take out to check, before I call out an engineer of might just check the heater element myself
 
just fit a short croc lead across L and N on the plug of the machine, then IR test to E. ( take plug out of socket first though. :81:)
 
just fit a short croc lead across L and N on the plug of the machine, then IR test to E. ( take plug out of socket first though. :81:)

I will when I have the time to remove the built in cupboard door, remove the plinth, remove the front decorative beading, remove closing mechanism, slide out WM......shouldn't have fitted the kitchen myself!
 
I've seen loads of appliances cause issues, TBH normally fridges and freezers.
Now I know its a disputed issue but officially you only ever test RCD with loads disconnected.
I myself query this for this exact reason

I have done EICR and tested RCD at board then out of curiosity done it at a socket and they fail.
Obviously on the sheets I recorded the official times with disconnected loads but still made an advisory on the report.
This is also another reason it's a shame they removed Cat 3 further investigation from the codes
 
Yep your right of course and I did on the previous tests I'd done on this socket/rcd, but for some reason I forgot to switch off my built in washer & diswasher. I would like to understand the reasons why the rcbo fails to do the x5. What is worrying is the the fact the rcbo is not functioning as it should. It makes you wonder what other devices are preventing rcd from working and perhaps good reason to carry at least one opeartion of an rcd with devices connected? Or should domestic properties be subject to PAT testing? Also perhaps a good reason to do regular MFT tests on RCD's, not just the push button.
 
Appliances connected to the circuit under test can interfere with the operation of the tester and cause it to produce incorrect results, even though the RCD / RCBO is OK. For example, white goods often have an LC filter connected directly to the flex, energised even when the power switch is off. This appears to the tester as capacitors between all its leads, which can affect its test current and calibration.

In this regard, the MFT will produce different results compared to the RCD test button because the circuit is different. As an example, suppose there is an N-E fault downstream of the RCD. When the test button passes current from the load side line to the supply side neutral, the imbalance will be more or less unaffected or even slightly increased and the RCD will trip. But an MFT plugged into a socket outlet can't get at the supply side of the RCD, so it dumps the current to earth. The N-E short might now decrease the imbalance at the RCD because some of the current can return by the neutral, so the RCD might not trip.

I would check the washing machine IR etc as you have said, but if it turns out to be OK, there is a possibility that varistors or Y-capacitors internally connected to earth are causing a similar effect on the tester as above.
 
Appliances connected to the circuit under test can interfere with the operation of the tester and cause it to produce incorrect results, even though the RCD / RCBO is OK. For example, white goods often have an LC filter connected directly to the flex, energised even when the power switch is off. This appears to the tester as capacitors between all its leads, which can affect its test current and calibration.

In this regard, the MFT will produce different results compared to the RCD test button because the circuit is different. As an example, suppose there is an N-E fault downstream of the RCD. When the test button passes current from the load side line to the supply side neutral, the imbalance will be more or less unaffected or even slightly increased and the RCD will trip. But an MFT plugged into a socket outlet can't get at the supply side of the RCD, so it dumps the current to earth. The N-E short might now decrease the imbalance at the RCD because some of the current can return by the neutral, so the RCD might not trip.

I would check the washing machine IR etc as you have said, but if it turns out to be OK, there is a possibility that varistors or Y-capacitors internally connected to earth are causing a similar effect on the tester as above.

This is my argument for why RCD should be tested with loads connected if is not going to operate when it's in use what's the point ?

It's great that it works with no load but then when in use fails to operate but this is a time old debate not for an overnight fix
 
Appliances connected to the circuit under test can interfere with the operation of the tester and cause it to produce incorrect results, even though the RCD / RCBO is OK. For example, white goods often have an LC filter connected directly to the flex, energised even when the power switch is off. This appears to the tester as capacitors between all its leads, which can affect its test current and calibration.

In this regard, the MFT will produce different results compared to the RCD test button because the circuit is different. As an example, suppose there is an N-E fault downstream of the RCD. When the test button passes current from the load side line to the supply side neutral, the imbalance will be more or less unaffected or even slightly increased and the RCD will trip. But an MFT plugged into a socket outlet can't get at the supply side of the RCD, so it dumps the current to earth. The N-E short might now decrease the imbalance at the RCD because some of the current can return by the neutral, so the RCD might not trip.

I would check the washing machine IR etc as you have said, but if it turns out to be OK, there is a possibility that varistors or Y-capacitors internally connected to earth are causing a similar effect on the tester as above.

I gather from what you saying is that the appliances are interfering with the MFT but in a real fault situation the RCD would still trip within the 40ms (As long has when the RCD was tested it operated correctly without any load connected).
 
I gather from what you saying is that the appliances are interfering with the MFT but in a real fault situation the RCD would still trip within the 40ms (As long has when the RCD was tested it operated correctly without any load connected).

That's my point, with the WM inadvertently connected, my MFT test showed the RCD test x1 56ms, x5 timed out at >40ms. So are we saying the RCD would trip? No it's TN-C-S.
 
....shouldn't have fitted the kitchen myself!

Careful the kitchen fitters dont find out you're doing that. Will add more weight to their argument for them fitting the electrics! Nah, forget it, they're gonna do the electrics anyway. Fit kitchens to your hearts content ......
 
to over simplify the situation, your MFT is basically trying to bung 150mA from L-E or N-E through the RCD. if you have a load connected, that is a parallel path down which a proportion of that 150mA can flow.add some capacitance and other electronic wizardry, and it will screw up your test. that's why you should perform RCD tests with loads disconnected- even with the circuit dissed from the RCD., although it's much easier to test at a socket, esp. if using auto-test.
 
This is my argument for why RCD should be tested with loads connected if is not going to operate when it's in use what's the point ?

It's great that it works with no load but then when in use fails to operate but this is a time old debate not for an overnight fix

That's fine when you're in fault finding mode but NOT when your conducting official RCD cert tests.
You are then testing the RCD compliance, not what's connected to the circuit, that the RCD is protecting.... Hopefully if you're conducting electrical tests in the correct sequence, thatall the other tests, would have already proved that circuit sound and in compliance...
 
Last edited by a moderator:
That's fine when you're in fault finding mode but NOT when your conducting official RCD cert tests.
You are then testing the RCD compliance, not what's connected to the circuit, that the RCD is protecting.... Hopefully if you're conducting electrical tests in the correct sequence, that
all the other tests, would have already proved that circuit sound and in compliance...

Yeah your right, this case I was just calibrating my mft and this fault would of come up on IR test.
 
I had this loads of times, its nothing to worry about, you should not have loads on the RCD'd circuit when testing, the WM is not making the RCBO faulty just the way the tester is putting the fault on and the WM is interfering with that, someone explained it to me but it went right over my head, its to do with the test equipment thats all.
 

Reply to RCBO X5 trip time out, caused by washing machine in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock