Correct as before they hit the load side where its balanced it goes through the electronics ,its like a wall between the supply neutral and the load neutral if you connect 2 load neutrals together it will trip just like in dual RCD boards when you have a shared neutral

When you say connect 2 load neutrals together are you meaning two different final neutrals from different circuits it will trip the RCBO's yea?
 
No... lol!! On a split board you are creating 2 separate RCD zones. The RCD's are also DP So separate line and neutrals to the 2 zones.... mix them and at lest one RCD will trip.


You can connect several RCBO's to the same neutral, be the lines from the same phase or all the phases... There is no imbalance seen because the neutrals are all the same, If you create a split system in the 3 phase DB and split the neutrals bars to suit, then you will have the same tripping problems as a split CU...


Not sure i explained that too well ....i know what i mean anyway...lol!!!
 
It looks to me that the Neutral is connected from the coil of the contactor and the Neutral bar of the DB.

All the Neutral bars throughout the installation are likely to be connected together (via the various submains/distribution cables, as this is before any of the RCBO's, this will have no effect, the contactor looks to be only switching the Line conductors and not through any RCBO's, the coils will be commoned in parallel to be controlled together.
 
No... lol!! On a split board you are creating 2 separate RCD zones. The RCD's are also DP So separate line and neutrals to the 2 zones.... mix them and at lest one RCD will trip.


You can connect several RCBO's to the same neutral, be the lines from the same phase or all the phases... There is no imbalance seen because the neutrals are all the same, If you create a split system in the 3 phase DB and split the neutrals bars to suit, then you will have the same tripping problems as a split CU...


Not sure i explained that too well ....i know what i mean anyway...lol!!!


AHHH yussss i hink ive got ya,Sorrrry blonde moment tonight folks :(, so does the phases have t be the same then or not can they be off different phases yea?
 
you do dont worry i just need to know about this bit "so does the phases have t be the same then or not can they be off different phases yea?"
 
I don't see why you cannot switch different phases for each contactor for it's own local circuit, or Item of equipment, or even all three phases for that matter if required.

The coil (control circuit) will have to be on the same phase if they are connected together (commoned)
 
Last edited:
AHHH yussss i hink ive got ya,Sorrrry blonde moment tonight folks :(, so does the phases have t be the same then or not can they be off different phases yea?

You can use any or all the phases, the neutral is the same neutral at the DB's It's only when you create a split zone as in the 17th split CU's with split neutral bars, you get the tripping problem....
 
You can use any or all the phases, the neutral is the same neutral at the DB's It's only when you create a split zone as in the 17th split CU's with split neutral bars, you get the tripping problem....
SO would all these RCBO's still be able to detect a borrowed neutral from another circuit, or will it not as the neutrals are all common to each other in this setup???
 
Think about it, ....the neutral is common to all 3 phases, so the sensing circuit won't see any imbalance. You can have a whole 36 pole 3 phase board with all single or multi phase RCBO's protecting every circuit, ....no tripping!!!
 
No, but they're not borrowing neutrals. Just imagine in your head that all neutrals in that building are connected to one HUGE neutral bar. (even though you view it as different neutral bars in the building.) so each RCBO neutral fly lead after going through the electronics is connected to the same neutral zone regardless of different boards hence no inbalance no tripping

Sent from my GT-I9100 using Tapatalk
 

Reply to Rcbo??? in the Australia area at ElectriciansForums.net

Similar Threads

Hi all, Wondering if you could offer some advice please. I carried out a small outdoor lighting project today at a commercial property. 4 lights...
Replies
5
Views
874
Hello all, I know this is very simple but I would like some advice please. I am installing a new circuit to feed 5 external floodlights. It is...
Replies
7
Views
3K
I had a call to a new customer who was experiencing what sounded like nuisance tripping on a kitchen ring. Some background first. It's an MK LN...
Replies
4
Views
712
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Hello, I'm not an electrician, more one of those 'competent DIYers', so probably the worst kind :) My electric shower broke, the shower firm came...
Replies
13
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock