Discuss RCBO's on a TT system. in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

HappyHippyDad

-
Esteemed
Arms
Reaction score
5,600
Morning all..

I am off sick from work, this rarely happens and already I am bored, so I thought I'd start a thread on the above which i have been thinking about.

Question 1: I realise that most on here suggest DP or SPSN RCBO's for a TT, but I am unsure why (with regards the regs)? This is why I am unsure:

537.2.2.1 states " A device for isolation shall isolate ALL live conductors from the circuit concerned, subject to the provision of Regulation 537.1.2" (which allows Isolation of the LINE only on TNS and TNCS systems as neutral is effectively connected to earth)

So the above reg is met by having a DP main switch as this reg is in relation to isolation, not disconnection due to fault.

531.2.1 "An RCD shall be capable of disconnecting all the line conductors of the circuit"

A Single pole RCBO accomplishes this reg.

This thread is solely to see if the standard single pole RCBO meets the regulations.

Question 2 : Also, I cant fathom why a SPSN would be acceptable whereas a SPSL RCBO wouldn't, you must be assuming disconnection from line by ADS (and therefore DP disconnection) as you wouldn't just switch the neutral? The benefits and sense of a DP RCBO are clear.

Cheers all :smile5:
 
Last edited:
It's because if you have an upfront 100ma s type RCD and single pole solid neutral RCBO's and there is a neutral/earth fault it will take out the upfront RCD as the neutral/earth fault won't be cleared when the RCBO has tripped. That's why you should use single pole switched neutral or double pole RCBO's.
 
Both SPSN and DP RCBOs are double pole the difference is SPSN RCBO is that it detects overcurrent in the Line only, whereas the Double Pole RCBO detects overcurrent in both line and neutral ...
 
Last edited by a moderator:
Both SPSN and DP RCBOs are double pole the difference is SPSN RCBO is that it detects overload in the Line only, whereas the Double Pole RCBO detects overload in both line and neutral ...
are you sure?
 
It's because if you have an upfront 100ma s type RCD and single pole solid neutral RCBO's and there is a neutral/earth fault it will take out the upfront RCD as the neutral/earth fault won't be cleared when the RCBO has tripped. That's why you should use single pole switched neutral or double pole RCBO's.

Well lets say we dont have an upfront RCD, would the single pole solid neutral RCBO meet the regulations for disconnection on a TT given the information in the OP.

Both SPSN and DP RCBOs are double pole the difference is SPSN RCBO is that it detects overcurrent in the Line only, whereas the Double Pole RCBO detects overcurrent in both line and neutral ...

You've confused me a bit there RG. Are you saying a SPSN (single pole switched neutral) is double pole?
 
Well lets say we dont have an upfront RCD, would the single pole solid neutral RCBO meet the regulations for disconnection on a TT given the information in the OP.



You've confused me a bit there RG. Are you saying a SPSN (single pole switched neutral) is double pole?

A SPSN is effectively DP as far as isolation is concerned, but is not the same as a DP RCBO/MCB, as has been pointed out earlier a SPSN has only one overcurrent sensing element in the line side, the N pole is just a linked switch. A true DP device has overcurrent sensing elements in both poles and are linked so either side with a fault will disconnect both.

A SPSN is fine for single phase circuits, a DP is usually used for say a 400V circuit where you have two lines and no N, or a 110V circuit where again you have two lines.
 
Thanks S68..

and thanks RG (sorry for not properly understanding how a SPSN RCBO worked).

I'd still be interested in if you/anyone had thoughts on whether a standard RCBO (not SPSN) meets the regulations for use as fault protection for TT given the regs stated in the OP?
 
happyhippydad;1085193]Well lets say we dont have an upfront RCD, would the single pole solid neutral RCBO meet the regulations for disconnection on a TT given the information in the OP.

There is no requirement for a 100ma S type RCD up front . But if you are relying on the RCBO's as earth fault protection it is prudent to install an up front time delayed RCD because if the RCBO fails you have a back up with the upfront RCD. Think about how many customer actually test their RCD quarterly........ Not many at all! If you do install an upfront s type RCD then you will have to install double pole or single pole switched neutral RCBO's as explained in my other post (IMO it would be silly not to install an upfront time delayed RCD).
 
Further information to post #8 :)

If we forget about the RCD part of the RCBO for the moment, which senses E faults or imbalances no matter which device is used as this is inherent to the way RCDs work, only the SPSN and DP types will actually disconnect the N, or second line in some cases, in the solid N types although the RCD part will sense a N-E fault and trip the device it cannot disconnect the N thus leaving the N-E fault present, and this will also trip any upstream RCDs.

Looking at the overcurrent parts of the device, in SP applications a SPSN device will suffice as in a L-N fault both the Line and Neutral will both see the same fault current and the device will trip via the overcurrent part in the line side, also a Line to E fault of sufficient magnitude would trip the overcurrent part even if the RCD part failed to operate, these devices have one pole marked as a N, as this is just a linked switch element in that pole.


With true DP types, if we again just consider the overcurrent parts of the device, consider a 400V circuit protected by DP device fed with say L1 and L2, now with a L1-L2 fault, both overcurrent elements in each pole will both see the same fault current and again will trip and disconnect both lines.
On this type of circuit though we have other possibilities for fault current paths, for instance an L1-L3 fault, an L2-L3 fault, an L1 or L2 to N fault, and an L1 or L2 to E fault, clearly the need for overcurrent protection in both poles is required to protect against these "extra" possible fault paths. On DP devices neither pole is marked N.

While the RCD part in a DP RCBO should in theory mitigate some of the conditions above where DP types are needed, the regs say we should not rely on RCD protection alone, plus the fact RCDs are not exactly failsafe or that reliable for that matter. ;)

You could replace a SPSN type with a DP type, but the converse is not true, where DP devices are specified they should only be replaced by DP types.
 
Thanks all,

I now feel more ill but at least I understand correctly the different types of RCBO available!

Still cant figure out if anyone has actually stated if an RCBO (solid neutral) meets the regs for a TT though! :confused:

I think, judging from everything I've read that it does. Better to use SPSN or DP but it does meet the regs.... I think!

ps.. I can almost hear you taking a big deep breath S68 and thinking, "ok, how can I write this any clearer?" :smile5:
 
A look at some manufacturers data sheets might help, I am sure I read somewhere that SP RCBOs were not suitable for TT use, it was from a major manufacturer if I recall.

One possible single phase use for true DP types would be for inside mobile caravans, where supplies from the various sites polarity wise may be a bit "suspect" ;)

They (DP types) are used a lot more in countries that don't have polarised plugs and S/Os.
 
Thanks all,

I now feel more ill but at least I understand correctly the different types of RCBO available!

Still cant figure out if anyone has actually stated if an RCBO (solid neutral) meets the regs for a TT though! :confused:

I think, judging from everything I've read that it does. Better to use SPSN or DP but it does meet the regs.... I think!

ps.. I can almost hear you taking a big deep breath S68 and thinking, "ok, how can I write this any clearer?" :smile5:

i think it's to do with both live conductors being isolated on a TT system in case of a fault. (N being regarded as a live conductor)
 
Shneider supply with their sp rcbos a warning label not to be used with TT or IT systems.

When they were first released the warning also warned for them not to be used with PME systems.
 
Here is a snippet taken from an online catalogue, it may also be buried somewhere on the Schneider site (which is a nightmare to find anything lol).

Schneider Electric A9D11820 iC60H 1 Module SP+N Type C RCBO 20A 10kA 30mA


The single-phase iC60H RCBO’s self-contained residual current device carries out complete protection of final circuits: protection against short-circuits and cable overloads, protection of persons against electric shock by direct contact (10, 30 mA sensitivities), protection of persons against electric shock by indirect contact (100 mA sensitivity), protection of equipment against fires set by leakage currents (100 mA sensitivity). The neutral is not interrupted when the device is tripped. Hence iC60H RCBO can be used on most circuits, except for the ones operating under TT or IT earthing systems.

I also think the same information was in MK literature.

I suppose an upfront TD 100mA RCD may make them suitable as far as the reg concerning disconnecting all Live conductors goes, as it would do with fuses in older boards, but then you have the problem that SP types don't disconnect the N-E fault which then trips the whole lot out as has already been said.


Edit: Rob beat me to it lol :)
 
Thanks all,

I now feel more ill but at least I understand correctly the different types of RCBO available!

Still cant figure out if anyone has actually stated if an RCBO (solid neutral) meets the regs for a TT though! :confused:

I think, judging from everything I've read that it does. Better to use SPSN or DP but it does meet the regs.... I think!

ps.. I can almost hear you taking a big deep breath S68 and thinking, "ok, how can I write this any clearer?" :smile5:





In the link posted by Tony is a post by Malcolm,he gives an answer to your question
 
Dredging up an old thread here.

Shortly have a board change on a TT supply to do. Normally I'd fit 100ma S Type up front and then dual RCD as I don't really see a big benefit in solid neutral RCBO's when you have an upfront RCD.

On this particular job I have a couple of distribution circuits in the consumer unit that I want to achieve good discrimination on. I was thinking of fitting a high integrity (normally use Hager) CU and fitting 2x Hager ADA932U RCBO (1P+N) on what would normally be the 'unprotected ways'.

Hagers website states they can be used in Consumer units but I'm unsure how they fit, being double width. Is it a case of just cutting off the busbar prong where necessary? Seems a bit heath robinson.

Anyone have any better ideas?
 

Reply to RCBO's on a TT system. in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hope this all makes as much sense as i can make of it and my "problem" can get sorted via some guru on here... Just a quick background on myself...
Replies
4
Views
915
I had a call to a new customer who was experiencing what sounded like nuisance tripping on a kitchen ring. Some background first. It's an MK LN...
Replies
4
Views
692
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
397
Carrying out a EICR in a commercial setting. In the main intake room the DNO supply comes in and it states clearly this is a PME system. 5 years...
Replies
5
Views
1K
OSG Pg.40 says: '[Split CU with 2x RCCBs] is not suitable for an installation forming part of a TT system as there is insufficient fault...
Replies
79
Views
7K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock