Morning all..
I am off sick from work, this rarely happens and already I am bored, so I thought I'd start a thread on the above which i have been thinking about.
Question 1: I realise that most on here suggest DP or SPSN RCBO's for a TT, but I am unsure why (with regards the regs)? This is why I am unsure:
537.2.2.1 states " A device for isolation shall isolate ALL live conductors from the circuit concerned, subject to the provision of Regulation 537.1.2" (which allows Isolation of the LINE only on TNS and TNCS systems as neutral is effectively connected to earth)
So the above reg is met by having a DP main switch as this reg is in relation to isolation, not disconnection due to fault.
531.2.1 "An RCD shall be capable of disconnecting all the line conductors of the circuit"
A Single pole RCBO accomplishes this reg.
This thread is solely to see if the standard single pole RCBO meets the regulations.
Question 2 : Also, I cant fathom why a SPSN would be acceptable whereas a SPSL RCBO wouldn't, you must be assuming disconnection from line by ADS (and therefore DP disconnection) as you wouldn't just switch the neutral? The benefits and sense of a DP RCBO are clear.
Cheers all :smile5:
I am off sick from work, this rarely happens and already I am bored, so I thought I'd start a thread on the above which i have been thinking about.
Question 1: I realise that most on here suggest DP or SPSN RCBO's for a TT, but I am unsure why (with regards the regs)? This is why I am unsure:
537.2.2.1 states " A device for isolation shall isolate ALL live conductors from the circuit concerned, subject to the provision of Regulation 537.1.2" (which allows Isolation of the LINE only on TNS and TNCS systems as neutral is effectively connected to earth)
So the above reg is met by having a DP main switch as this reg is in relation to isolation, not disconnection due to fault.
531.2.1 "An RCD shall be capable of disconnecting all the line conductors of the circuit"
A Single pole RCBO accomplishes this reg.
This thread is solely to see if the standard single pole RCBO meets the regulations.
Question 2 : Also, I cant fathom why a SPSN would be acceptable whereas a SPSL RCBO wouldn't, you must be assuming disconnection from line by ADS (and therefore DP disconnection) as you wouldn't just switch the neutral? The benefits and sense of a DP RCBO are clear.
Cheers all :smile5: