Discuss RCBOs with 1 flying wire. in the Electrical Forum area at ElectriciansForums.net

Welcome to ElectriciansForums.net - The American Electrical Advice Forum
Head straight to the main forums to chat by click here:   American Electrical Advice Forum

Bul

-
Reaction score
10
Do RCBOs normally have 2 flying leads - neutral and earth?
Are there "old" rcbos and new types.

The reason I ask is that I have bought Proteus RCBOs and they have a flying neutral wire only.

I've never fitted RCBOs before and am just a bit confused.

Any explanations appreciated.

Bul
 
sorry to go off track slightly but when connecting an rcbo do you guys normally use a seperate earth terminal for the functional earth or use the same connection as the cpc for that circuit?
 
same terminal for clarity, besides if you've got a board full you'll have no choice
 

Reply to RCBOs with 1 flying wire. in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock