- Reaction score
- 20
I tested a customers BS4293 MEM 100A, 30mA RCD, which is about 25 years old, after it tripped overnight. The trip time at x 1 was 207.2, 78 and 54.2 ms at 0 deg. and 68.6 ms at 180 deg. I know that the limit is 200 ms, so one reading was slightly over, which is why I repeated the test. At x 5 it tripped at 50 ms at 0 deg. and 41.5 ms at 180 deg. So, again both over the limit of 40 ms. No trip at x 1/2.
Do these results mean I have to change the RCD? Or is there any tollerance? If so, can only get used identical replacement from the internet. Or should I change it to a RCD to BS EN 61008-1, like a Wylex 100A 2 Pole 30mA RCD?
Do these results mean I have to change the RCD? Or is there any tollerance? If so, can only get used identical replacement from the internet. Or should I change it to a RCD to BS EN 61008-1, like a Wylex 100A 2 Pole 30mA RCD?