Farm job im at has a problem


three phase tt system comes into main barn area, three phase main distribution board (with 100mA s type 4 pole rcd as main switch) supplying barns and general farm buildings

Swa single phase supply to farm house(around 40meters away), supplied directly from meter side of distribution board on henly blocks to switchfuse/rcd

so house supply is totally independent from the barn supply

however everytime there is a fault on the barn distribution board and its main rcd operates it takes out the rcd at the farm house too

i havent been over to the farmhouse yet but i cant understand why it would be knocking out the rcd in the house?

any ideas?
 
Where abouts is the suppliers transformer ...is it close up a pole?
What kind of rcd's are they - are they modern type that measure inbalance between L/N?

Have you ensured all your customer side connections are sound and tight... check busbar tabs are on the correct side of any mcb, rcd and main switch terminal clamps.
 
If the SP supply is taken from the load side of th e TP RCD the any fault on the SP supply will trip the TP RCD
 
As I read it Pete the house SP supply comes off before the 3P RCD so they should not effect each other. Which is the problem the OP is trying to get a handle on as to why they actually are!
 
If theres a single earth stake in use for both barn and house , and all bonding is done at the house , it could be the Ze of the earth stake is higher resistance than the bonding at the house and fault currents are back fed to house , just a thought,,
 
This reads plain to me but a few are not reading the OP properly ...

At mains there is a 3ph board with 100mA rcd main switch
Also a 1 phase supply straight of the meter via a henley block to a sw/f + RCD ...lets assume 100mA

When a fault trips the rcd of the 3ph board the rcd IN THE house trips so assuming a 30mA is tripping in the house possibly 17th edition board.... can the OP confirm this!?


Edit confirmed in post 15.
 
he said henleys, switchfuse, rcd.

then i hear TP board and TT the first thing i think of, is the first (RCD) enclosure insulated?
 
This reads plain to me but a few are not reading the OP properly ...

At mains there is a 3ph board with 100mA rcd main switch
Also a 1 phase supply straight of the meter via a henley block to a sw/f + RCD ...lets assume 100mA

When a fault trips the rcd of the 3ph board the rcd IN THE house trips so assuming a 30mA is tripping in the house possibly 17th edition board....






can the OP confirm this!?






Thats how I read it as well ...
 
I thought I had read it right, what I thought was, "what is protecting the single phase supply"? it is from henley blocks to a switch fuse then to the house where there is a rcd?? or does he mean there is a rcd in the barn at the supply, oh dear I am now getting confused too
 
Where abouts is the suppliers transformer ...is it close up a pole?
What kind of rcd's are they - are they modern type that measure inbalance between L/N?

Have you ensured all your customer side connections are sound and tight... check busbar tabs are on the correct side of any mcb, rcd and main switch terminal clamps.

rcds/mcbs are mem old 3871/4293 type, dunno about house end ive not been able to get access in there yet but assuming they are of similiar age

also not sure of tx location
 
This reads plain to me but a few are not reading the OP properly ...

At mains there is a 3ph board with 100mA rcd main switch
Also a 1 phase supply straight of the meter via a henley block to a sw/f + RCD ...lets assume 100mA

When a fault trips the rcd of the 3ph board the rcd IN THE house trips so assuming a 30mA is tripping in the house possibly 17th edition board.... can the OP confirm this!?


Edit confirmed in post 15.


Spot on darkwood yes 100mA s type sp protecting submain(this is holding fine but the 30ma rcd in house is tripping out with the 3pn board in the barn)
 

Reply to Rcd head scratcher in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
For context i am in my 2nd year in college and my head is going round in circles a question in my project for which i need to select the right...
Replies
22
Views
4K
The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Replies
18
Views
2K
Hi all, Merry Christmas to everyone, and apologies for talking work during the holidays😅 I have my first EV charger install job early in the New...
Replies
14
Views
2K
I may be seeking the holy grail here, but does anyone have any instant thoughts for a compact 3 phase distribution board that doesn't cost the...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock