So you are saying it would be more likely a faulty RCD rather than a Circuit fault? Disagree

I was disagreeing with the post that ruled out a faulty RCD ....

Tripping RCD's can be caused by:

1. Issue with the incoming supply
2. Faulty RCD's
3. Earth leakage from appliances
4. N-E faults on RCD circuits
5. N-E faults on non RCD and RCD circuits
6. Faulty appliances

etc etc
 
The shower is still working but doesn't get used? The Neutral and earth are still connected even if the MCB is switched off (others have mentioned this). When RCDs trip I always think water or poor insulation resistance. I'd be tempted to remove the shower neutral & earth (and tape up) in the first instance unless it can be totally isolated? This will eliminate that circuit without an unnecessary disruption to circuits that are being used.
It does seem odd to wire the RCD in with circuits either side rather than just to the right with one length of bus bar - looks like it's been an afterthought.
 

Reply to RCD in consumer unit keeps popping, replaced with new one, still same issue in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

HI My flat just failed the EICR because there is no RCD in the consumer unit. There is no space for a new RCD as the consumer unit is full. Do I...
Replies
18
Views
2K
Hi All, I am in the middle of purchasing a small 1 bed flat in England, and have been sent a Domestic Electrical Installation Certificate by the...
Replies
1
Views
1K
Hi, The `power went out throughout the house this afternoon but only to the sockets, the lighting circuits are all fine. I went to the consumer...
Replies
9
Views
1K
Ok, most new Consumer unit seem to come with a 63A RCCB and two MCBs. Most house consumer units now will also have RCD of some type be it a dual...
Replies
24
Views
1K
Hello, Is there an actual age limit on house wiring that would prevent a traditional fuse box being replaced with a consumer unit please...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock