Hi all. Ive been testing a flat with a main switch consumer unit and a mixture of mcbs and rcbos.

All test perfect until rcd test for kitchen ring rcbo its a wylex b32a rcbo.

With cables connected to rcbo but nothing plugged in it gives readings of >300 for x1 and >40 for x5
Then when cables disconnected the readings are fine. 2 other rcbos in board and they are fine. Tried two other rcbos and same problem occurs. Has anyone came accross this before?
Thanks
 
Tn when cables disconnected the readings are fine.

that's the correct way to test, without any circuit/equipment affecting the trippin gtimes. if readings are good, then that's it. end of.

 
Thanks, its the first time ive seen it. Theres only 3 points on the circuit 2x double sockets and a 20a dp for a fridge. Its an empty flat so nothing plugged in atall. Thanks again
 
Possible crossed rings / bridged circuits. The IR might test fine on its own but there's a parallel path back to the board when one of the other circuits is also energised.
 
I would agree something is affecting the RCBO. I've left an appliance mistakenly connected, and had a neutral- earth fault also, that stopped my MFT testing an RCD.
 
Likewise, I have had faults on connected circuits preventing RCDs from operating when tested with circuits connected.
 
Hi all. Ive been testing a flat with a main switch consumer unit and a mixture of mcbs and rcbos.

All test perfect until rcd test for kitchen ring rcbo its a wylex b32a rcbo.

With cables connected to rcbo but nothing plugged in it gives readings of >300 for x1 and >40 for x5
Then when cables disconnected the readings are fine. 2 other rcbos in board and they are fine. Tried two other rcbos and same problem occurs. Has anyone came accross this before?
Thanks
Guess there is something wrong with the circuit connected to the RCBO then, answer the circuit needs a complete electrical test.
 
It was a small rfc with only 3 points. I had tested end to ends, R1+R2 IR then zs and all had no adverse readings until i got to the rcd test. It was a kitchen circuit in a care home all points were fed via conduit drops
 
You wouldn't think a bodge like that would happen in a Council property eh ? But I still don't see what was bypassing the RCD tripping coil when all tests on the circuit were spot on.
 

Reply to Rcd issue head scratcher in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I had a call to a new customer who was experiencing what sounded like nuisance tripping on a kitchen ring. Some background first. It's an MK LN...
Replies
4
Views
713
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
I will start with apologies, as I have not thought this through very much (at all) yet and have just sat down with a beer.... meaning I thought...
Replies
3
Views
1K
Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
608

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock