Discuss rcd meter tails in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
8
hi i tested a domestic property earlier,and someone has sunk the meter tails,the fb is a 17th edition,my question what size external rcd is required for the meter tails,its a pme system,many thanks
 
"sunk the meter tails"????? more info. needed.

if you mean that the tails are buried in plaster < 50mm deep, you need a 30mA RCD. that buggers you up as regards discrimination.
 
a time delay would not comply. you say you.ve tested the installation. code C3 ( 522.6.101 ) END OF.
 
i have those options to the customer,they want nothing surface in trunking etc,they want the rcd optionso does the rcd have to be time delayed ?
theres no mechanical protection to them buried tails.....
so where you getting time delayed from?....
look, you have obviously made your mind up so you go do what you want....
 
They are askjing you to do something contrary to the regs. So it's a no-go. To comply with 522.6.101, you would need to fit a 30ma non-delay rcd. This would mean you'd have 2 similar rcds in series. Basically you're snookered.
 
tell them NO,NO,NO. you work to regs. regs. say notee puttee 2 similarloee rcds in the series configurationone, so you don't.
 

Reply to rcd meter tails in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I was hoping someone with a little more insight might be able to shed some light on a potential issue I have, as I can't seem to find another...
Replies
75
Views
7K
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
Hi there, I built a house with ground source heating 5 years ago and it's a fairly large house so I have 3 phase supply 80 amps per phase. I had...
Replies
7
Views
927
Hi guys, could someone help with the following please? The scenario is: Domestic property supplied via three phase (with a 3P main DB, NO SPD)...
Replies
2
Views
487
Can someone sanity check my thinking please.... An 80 amp PME service head, tails to meter, 25 sq mm tails into an enclosed fused isolator with...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock