Had a strange one today, hager 100a 30ma rcd failed to trip with the tester. TT earthing arrangement, also very strange readings. ze 197.4 ok normal for around that area the zs around 0.53. Went and got a replacement 80a 30ma rcd, the 100a was on the large side. Failed the test again. Went home pulled out the cupboard an older hager 80a 30ma rcd the ones that took up 4 module slots and it tested fine, all other circuits were disconnected. Can't see how it would be a neutral to earth fault unless I put the circuits back one at a time to see if one causes a problem...just not sure.
 
Zs prob caused by parallel path via main bond conn'd to neighbours who happen to be TN.

If it failed with the tester, them its duff or the tester is. Imho
 
Don't think it's me tester. Calibrated the other week and works on other rated rcds

a good point you make about the zs tho. I was unable to explain this to myself. I did try this older rcd and that tested fine. I sometimes wonder about wholesales do they think it'll be funny to take one from the faulty shelf...
 
Don't ever be surprised that a replacement RCD device is as faulty as the unit it's replacing, seen that happen far too many times, as well as a complete package box of them being faulty!!

When you come across units that won't trip under test, operate the units test button a few times to free up the the internal mechanism, wait a few minutes and try testing them again. Sometimes the contacts and.or internals stick.

Having said that, i have an inherent distrust of anything that fails testing straight off the bat so to speak. If it can happen once when testing, it can happen again in service when it's actually needed to operate!!
 
When you come across units that won't trip under test, operate the units test button a few times to free up the the internal mechanism, wait a few minutes and try testing them again. Sometimes the contacts and.or internals stick.

Having said that, i have an inherent distrust of anything that fails testing straight off the bat so to speak. If it can happen once when testing, it can happen again in service when it's actually needed to operate!!

Agree with your second paragraph. Anything as safety critical as an RCD or MCB that doesn't work right first time straight out of the box without cajoling is suspect and unfit for purpose and should be returned for replacement or refund. This ties in with the RCD testing best practice of checking whether the RCD tester trips it correctly BEFORE going anywhere near the test button, and failing it if it doesn't.
 
The fastest testing 30mA RCDs I have had to pleasure to test are the relly old Wylex ones that are the size of a house brick.

they don't make stuff like in the old days
 
could these RCDs be ones that require a couple of short tails fitted for testing?
 
could these RCDs be ones that require a couple of short tails fitted for testing?

Wylex rcbo's have this problem. You insert your probe into the neutral terminal and you think its made contact with the screw but it hasnt. You need to fit an adaptor that I believe you can buy, or make one as I have done. But then again, if the OPs probe wasnt touching the neutral, it wouldnt even carry out the test.
 
Wylex rcbo's have this problem. You insert your probe into the neutral terminal and you think its made contact with the screw but it hasnt. You need to fit an adaptor that I believe you can buy, or make one as I have done. But then again, if the OPs probe wasnt touching the neutral, it wouldnt even carry out the test.

?

Take the end off probe?

If that doesnt work push it in with cable
 

Reply to RCD not tripping on test in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
315
What should you do if a client has a CU that is a split board protected by 2 * 63Amp 30mA double pole RCCDs, you took Zs and tested both RCCDs by...
Replies
22
Views
2K
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
778
Keeping this brief.....................New dwelling.....TT system with 100mA S type rcd protected supply to local board with 30mA RCD. Freelance...
Replies
21
Views
3K
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock