Called to investigate nuisance tripping. One 30ma rcd protecting tt installation. Insulation resistance just under 1 megohm with everything plugged in. Unplugged everything but tripping intermittently for no apparent reason. Rcd test all ok ramp test trip at 23ma. Is it possible for rcd itself to have intermittent fault? It's an old large grey wylex one. Could swear I heard fizzing in cupboard. But all breakers tight. It's a good metal merlin verdin one.
 
Just under 1meg ohm usually wouldn't trip RCD, did u say it was tripping when not under load, how about a clampmeter on the main earthing conductor see if you have leakage to earth, if so clamp around each cpc, it's also very possible the RCD has failed, I took one of those out last year because if was tripping occasionally, change the RCD it's s starting point?Good luck
 
Hi,
Do a ramp test to confirm trip current, as some rcds can become more senstive with time.

Remind me you have done one, check all applainces, check that there are no NE shorts, note that class I appliances may leak up to 3.5mA each to earth, and class II may leak 0.25mA. also check imersion heaters and central heating pumps. Use an earth leakage clamp meter to measure the leakage current.
 
Last edited:
Very few domestic situations would utilise a S type RCD because of cost factors, they normally would be just a normal 100mA type. They were used in TT situations and in some cases TN-S situations because of the high Ra/Ze values and therefore the high Zs values.
 

Reply to Rcd nuisance tripping in the Australia area at ElectriciansForums.net

Similar Threads

Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
778
I'm writing this mainly hoping something occurs to me while writing it! I got called to an occasionally tripping RCD. It's a Hager double height...
Replies
19
Views
2K
Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
Replies
19
Views
1K
Hi, I seem to have an RCD that keeps cutting the power at random times without actually tripping, if I reset it, the power comes on and will stay...
Replies
7
Views
443
Keeping this brief.....................New dwelling.....TT system with 100mA S type rcd protected supply to local board with 30mA RCD. Freelance...
Replies
21
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock