Hi all,

Half way through an installation as a subby on someone else’s electrical contract.

It’s for a church, in which they’ve asked me to run 2 radial circuits.

Circuits 1 and 2 split a total of 10 fused spurs, 5 on each radial, each with a 3a fuse and on a 20a mcb.
Cables are run under floor boards and through the joists.
Run in 2.5mm twin and earth, each run no longer than 25m.

I’m under the impression that this needs to be RCD protected but the site manager has said that MCBs are fine. I’ve flicked through the regs but haven’t sat my 18th yet, which is booked in for next month.
As the cables aren’t in walls or supplying any sockets, he may be right?

Can anyone shed any light on this please?
 
If the circuits do not need additional protection in accordance with 415.1.1 or earth fault protection by an rcd say 100mA etc and they are not supplying sockets then yes he is correct going from your information provided.
As they are fused spurs then they are just supplying fixed current using equipment by the sounds of it.
That’s all I can say given your information.
 
Hi all,

Half way through an installation as a subby on someone else’s electrical contract.

It’s for a church, in which they’ve asked me to run 2 radial circuits.

Circuits 1 and 2 split a total of 10 fused spurs, 5 on each radial, each with a 3a fuse and on a 20a mcb.
Cables are run under floor boards and through the joists.
Run in 2.5mm twin and earth, each run no longer than 25m.

I’m under the impression that this needs to be RCD protected but the site manager has said that MCBs are fine. I’ve flicked through the regs but haven’t sat my 18th yet, which is booked in for next month.
As the cables aren’t in walls or supplying any sockets, he may be right?

Can anyone shed any light on this please?
You might want to check if PVC/PVC cables are suitable for Churches, seem to recall there are certain rules regarding Churches, could be wrong but worth checking, was this work designed and planned prior to 2019?
Wiring churches: the engineer's perspective - https://electrical.------.org/wiring-matters/issues/53/wiring-churches-the-engineers-perspective/
You may find this useful
 
Last edited:
Sorry, should have added, where cables are not under the floorboards, they are in pvc trunking, fixed in securely with D clips.

The spurs supply power to a radiator fan, so fixed equipment and won’t be used for anything else.
Spurs are fixed to the walls and are located in the main hall along the sides of the walls.

Unsure of when the work was planned.
 
I posted up concerns from Engineers regarding wiring in Churches, what to avoid processes to follow, Authorities responsible, etc the OP hasn't responded I can only imagine He/ She is at work, the OP is a subby but it's still the OP's responsibility to take note of the advice given in the linked document, look forward to the response.
 
RCD protection is not required, unless any of the appliances supplied are mobile and to be used outdoors.
Additional protection (excluding RCDs) will be required for the cables run through joists.
i.e. hole for the cables at a depth greater than 50mm, metal plate over any notches or holes less than 50mm, cable with an earthed metallic sheath, etc.
 
You might want to check if PVC/PVC cables are suitable for Churches, seem to recall there are certain rules regarding Churches, could be wrong but worth checking, was this work designed and planned prior to 2019?
Wiring churches: the engineer's perspective - https://electrical.------.org/wiring-matters/issues/53/wiring-churches-the-engineers-perspective/
You may find this useful

Pete, I think it only matters if the church in question is listed, I've worked on a couple in the past where one was and one wasn't so yes the op needs to know which it is.
 
Pete, I think it only matters if the church in question is listed, I've worked on a couple in the past where one was and one wasn't so yes the op needs to know which it is.
OK, thanks, but a reply from OP would be nice agreeing or disagreeing makes no difference,
The OP is currently Offline, so perhaps I'm a tad premature in my post, but hey Hoh, never mind worse things happen at sea.
 
Last edited:
OK, thanks, but a reply from OP would be nice agreeing or disagreeing makes no difference,
The OP is currently Offline, so perhaps I'm a tad premature in my post, but hey Hoh, never mind worse things happen at sea.
I was just trying to get involved in the thread Pete, I'll keep my gob shut from now on and stick to Admin duties.
 

Reply to RCD on radial for fused spurs? in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

HI All, I am building a new house (self build) and have my part P so am running the cabling. My reading of the regs says that any appliance of...
Replies
18
Views
4K
Hi all. Have an issue i'd love some advice on if anyone would be so kind. Will try to be brief. Thank you!! So, have an intermittent RCD trip at...
Replies
43
Views
3K
Hello all. I have just bought my first house but it needs a bit of work. I am re-wiring it and I've found the conservatory ring has been spurred...
Replies
11
Views
2K
A recent EICR turned up a fault: an RCD fused spur was feeding a socket and a shower pump, and neither socket or pump had continuity on the CPC...
Replies
17
Views
3K
Hi guys I have some industrial lighting circuits to wire in a workshop and was after some fresh ideas/suggestions as to how i could best do this...
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock