Hi Guys.

I have a new build house waiting for the meter to be fitted by the NIE. What are the requirements for isolation in the outside metering cubicle on a tt system. Would a 100a isolator be ok or do I need an RCD here as well as the 2 x 30mA ones in the con unit.
Con Unit is back to back with the meter cubicle, tails through wall in conduit and everything is plastic.

Whats the correct method please,

Davy
 
Well there is no need for any outside isolation to be fitted at all that is totally your call, unless the DNO have asked you to to this.

Because it is a TT system your correct that there is every chance you will need to provide RCD protection for additional protection for ADS, as well as all the other reasons outlines in the regulations.

As your tails are coming through the wall and not buried, then into an insulated enclosure there is no need to have that isolator to be an RCD

There is of course an argument for a better design to fit regardless of need perhaps a 100mA time delayed or S typoe RCD upfront. This will definitely give you added protection on the 30mA RCDs, as well as flexibility in the installation for say an outside supply in future.

Of course the extra 100mA RCD, especially a time delayed one is going to add cost
 

Reply to Rcd or isolator. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
D
Hi, I have received conflicting advice about Main Isolator Switches and would appreciate forum member's help to plan a way ahead. Looking to the...
Replies
5
Views
2K
Deleted member 155212
D
Hi all -- full disclosure I am a 'DIY-er' but wanted to post here for greater visibility seeing as I certainly won't be doing this work myself...
Replies
21
Views
4K
The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Replies
18
Views
2K
D
Hi, I have received conflicting advice about Main Isolator Switches and would appreciate forum member's help to plan a way ahead. Looking to the...
Replies
0
Views
977
Deleted member 155212
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock