fitted a 12 way split board in place of old 6 way re wirable. 2 light circs, one ok, other trips rcd. dis board has 2 ways off main switch and 5 ways off each rcd. time was running out so i tried faulty circ on one of the 2 ways off main switch. mcb held but still took out one rcd. i split light circ in two and got half lights working, connected other half and rcd trips, mcb ok. all lights work if rcd is off. before you ask i had already put neutral of faulty circ into main neutral block. Dis board is Contactum , cheap, i know ! any help guys ? cheers.
 
The only thing you can really do is carry out an Insulation Resistance test on the lighting to try and find the faulty leg(s). the half that you got working can be left alone, the other half remove all lighting connections and perform IR on each leg and hopefully you'll find the faulty one which you'll have to replace. Hope this helps.
 
Try both lighting circuits from the same RCD, neutrals in the same bar, that will show you if you have a borrowed neutral (favourite).
 

Reply to rcd problem in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
317
Doing a kitchen job for my daughter’s music teacher, who also happens to have been in my wife’s class at school. Nothing big… just a little...
Replies
2
Views
229
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Replies
13
Views
1K
Hi, I can't get an RCD to switch on at all, even with the main isolator switched off. Is that definitely a faulty RCD or could it be something...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock