    hi guys if a bank of 20 sockets wired in surface trunking on a radial circuit,these sockets would be used for computers gameboys and music equipment,my question is would they need to be rcd protected ? i know normally they would not,it's just that my mate said if protecting computers they should, i cannot find anything on this
     
  2. Pete999
    Online

    Pete999 Forum Mentor

    Location:
    Northampton
    Business Name:
    None
    If the said socket outlet circuit is subject to high earth leakage current then the circuit needs to be wired differently than a normal Ring FC or Radial FC as per Regulation 543.7.1.201 information can be found on page 81 OSG and Figures 7.5.3 (1) and 7.5.3 (11) Page 82 OSG
     
    • Informative Informative x 1
  3. deanmac
    Offline

    deanmac Regular EF Member

    i would be running a separate earth along with dual earth terminals just cannot see anything regarding rcd
     
  4. telectrix
    Online

    telectrix Scouser and Proud of It Respected Member

    Top Poster Of Month

    Location:
    cheshire/staffordshire
    Business Name:
    Telectrix
    to omit RCD protection for these sockets, you would have to do a written risk assessment justifying a reason why. what's to stop someone plugging in a faulty appliance?
     
  5. Wilko
    Online

    Wilko Electrician's Arms

    Location:
    Berkshire
    Business Name:
    Wilko Electrics
    Hi - As Pete has said.
    For RCD see Reg 411.3.3 :)
     
  6. deanmac
    Offline

    deanmac Regular EF Member

    these sockets are for my friend and will be solely for computer and stereo equipment and not for outdoor purposes etc
     
  7. Midwest
    Offline

    Midwest Electrician's Arms

    Location:
    Oxfordshire
    Isn't the risk assessment, not for residential (apologies for my grammar) and no longer current in the 18th?
     
    • Agree Agree x 4
  8. spinlondon
    Offline

    spinlondon Forum Mentor

    Location:
    Harlow Essex
    Unless the sockets are intended for specific items of equipment, they will need RCD protection.
    Haven’t gotten round to checking whether the 18th has changed this.
     
  9. deanmac
    Offline

    deanmac Regular EF Member

    just for the items mentioned
     
    • Bad Spelling Bad Spelling x 1
  10. Murdoch
    Offline

    Murdoch Regular EF Member

    Location:
    Woking
    I thought that the 18th made rcd's mandatory on sockets and lighting circuits ...
     
    • Agree Agree x 8
  11. deanmac
    Offline

    deanmac Regular EF Member

    i thought not for sockets if a risk assessment has been done
     
    • Disagree Disagree x 5
  12. spinlondon
    Offline

    spinlondon Forum Mentor

    Location:
    Harlow Essex
    Risk assessments do not apply to domestic installations with regards to omitting RCD protection.
     
    • Agree Agree x 5
  13. spinlondon
    Offline

    spinlondon Forum Mentor

    Location:
    Harlow Essex
    Are these items likely to be unplugged and perhaps taken to other locations?
     
  14. deanmac
    Offline

    deanmac Regular EF Member

    so even though these sockets will be wired surface and only used for computers they will need rcd protection ?
     
  15. westward10
    Online

    westward10 In echoed steps I walk across an empty dream. Staff Member Moderator

    Location:
    Northamptonshire
    It is still in the 18th Ed.
     
Loading...
Similar Threads - protection sockets Forum Date
RCD Protection for submains Electrical Forum Feb 11, 2019
Protection to be used on a 5KW motor??? Electrical Forum Feb 8, 2019

Share This Page

Users found this page by searching for:

  1. rcd protection on socket

Electricians Directory Post a Domestic Job Post a Commercial Job