Discuss rcd protection in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
9
EICR
tnc-s system ....lighting circuit ......cables buried less than 50mm ....not rcd protected....what code should i put
(i think code 2...
but could it be c3 (not compliant with current regs)
 
C2 is potentially dangerous.
C3 is improvement recommended.

What potential danger are you seeing here that warrants a C2?

The most I would give that on its own, assuming no other problems having an impact on it, is C3
 
Thinking about metal fittings

irrelevant. metal fittings without a cpc would be a code C2 , but if the installation was pre 2008, the 522 6.101 did not apply , so the most you can give is a C3 for lack of RCD.
 
Yet another incompetent inspector!

When will it end?!

Scott 123, you shouldn't be carrying out periodic inspections if you have to ask these kind of questions.
 
I think maybe it is time to to start applying codes to some of the people Carrying out Eicr's.
With the Op getting a C1
 
Code zero even!
If it wasn't so sad Damian it would be funny just how many people can't seem to code an installation correctly.
 
he couls always get a job with british gas. anything done to 16th is an instant C1, new CU necessary.
 
There's one round my way, calls himself Bradbury Electrical. He's fresh out of college, can't be older than about 20, and drives a liveried up van with 'testing and inspection specialist' written all over it. Amongst other blunders, this kid C1s 6mm bonding conductors on 60A TN-S systems. I've yet to bump into this clown in the wholesalers but I look forward to the day I do!
 
These examples can swing both ways. Time served sparky (now in his seventies), 'man and boy' etc. Not updated since the 15th Ed because he knows everything. 4 x code 1's and 2 x codes 2's on an EICR. He then grades it satisfactory (repairs not done)!

Puts in a new board for the customer in May 2014 to 15th Ed Regs. Boards hanging off the wall, covers hanging off the board and no certification.
 
So after attending college and training with a so called time served electrician who was crap ..what should I do ... Retrain with another crap electrician or use the knowledge and qualifications I have gained along with asking for pointers on this forum for guidance to better myself...I've asked for pointers not for u to do the job... Thank you to those who gave helpful answers .and if the unhelpful ones are so good at the job how have you got so much time to spend on here abusing others (to make yourselves feel superior)
 
So after attending college and training with a so called time served electrician who was crap ..what should I do ... Retrain with another crap electrician or use the knowledge and qualifications I have gained along with asking for pointers on this forum for guidance to better myself...I've asked for pointers not for u to do the job... Thank you to those who gave helpful answers .and if the unhelpful ones are so good at the job how have you got so much time to spend on here abusing others (to make yourselves feel superior)

C1 for this post mate !!!!:seeya:
 
So after attending college and training with a so called time served electrician who was crap ..what should I do ... Retrain with another crap electrician or use the knowledge and qualifications I have gained along with asking for pointers on this forum for guidance to better myself...I've asked for pointers not for u to do the job... Thank you to those who gave helpful answers .and if the unhelpful ones are so good at the job how have you got so much time to spend on here abusing others (to make yourselves feel superior)


Have you read and diested the guides on this link?

Best Practice Guides - Electrical Safety First
 
So after attending college and training with a so called time served electrician who was crap ..what should I do ... Retrain with another crap electrician or use the knowledge and qualifications I have gained along with asking for pointers on this forum for guidance to better myself...I've asked for pointers not for u to do the job... Thank you to those who gave helpful answers .and if the unhelpful ones are so good at the job how have you got so much time to spend on here abusing others (to make yoursetter myself...I've asked for pointers not for u to do the job... Thank you to those who gave helpful answers .and if the unhelpful ones are so good at the job how have you got so much time to spend on here abusing others (to make yourselves feel superior)

Get experience working along side an experienced inspector. You have no excuse, just because you once worked with a poor electrician that doesn't mean that you can go throwing yourself head first into jobs that you don't know how do do.

Here's some helpful advice for you; learn how to walk before you start running.


and if the unhelpful ones are so good at the job how have you got so much time to spend on here abusing others (to make yourselves feel superior)

It's not abuse fella, it's the hard truth. In terms of inspection and testing knowledge, mine is already far superior to yours, therefore I don't feel the need to do anything to make myself 'feel' superior. That superior knowledge gives me the ability, and the right, to say that you currently don't posses the level of knowledge needed to be carrying out inspection and testing work if you have to be asking such basic questions. You can't just take the work on and expect people on forums to answer questions, that you, as an electrician who has taken money in exchange for testing and inspection services, should know!

Finally, as you asked, I have time to spend on here in between emailing invoices to my many customers, customers whom I have gained over many years who give me money to carry out work that I can actually do, and do bloody well!
 

Reply to rcd protection in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
679
I'm obviously still new and learning about what I can and cannot do, but essentially I want to install an EVSE at my own house for an electric...
Replies
8
Views
531
Hello! I've been racking my brain this evening about some RCD selections. I've been doing some work for a solar installer, and they've asked me...
Replies
5
Views
877
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
Hi there , Currently doing a college project where i need to select protective devices for the contract. I'm now at the point of selecting SPDs...
Replies
5
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock