R

roukel01

Went to inspect a rented property the other day.

TNC-S, Consumer unit has RCD as main switch protecting all circuits. Not too keen on the idea of one RCD (16th edition install about 10 years old), but anyway that wasn't really my concearn. The RCD was only rated at 63amps and it had the following circuits connected:

45amp cooker circuit
4 x 32amp ring circuits
4 x 6amp lighting circuits

although the RCD didn't show any signs of burning out etc, I gave it a code 2 as I think it requires uprating to at least an 80amp RCD.

Now, if I get the go ahead to change the RCD, because I am altering the board slightly, am I required to bring it upto 17th edition (ie split the circuits up onto two RCD's or pop the circuits on RCBO's) or can I simply change the existing RCD for an 80amp type???

Thanks all
 
Not sure how you could justify a code 2 without confirming the size of the main fuse.

I agree but even more importantly, the installation has been in use for 10 years without any signs of damage and with diversity, that 63A rated device will be more than adequate. Code 4 for me.
 

Reply to RCD rating too low in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Did a couple of inspections on 2 x 2 bed ground floor flood damaged flats today, only 4 circuits in each, bizarrely one socket circuit and 2...
Replies
6
Views
2K
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K
For context i am in my 2nd year in college and my head is going round in circles a question in my project for which i need to select the right...
Replies
22
Views
4K
Firstly, thank you for taking the time to read this. I am not trained in electrics whatsoever, I am a just a home owner looking for advice. I...
Replies
2
Views
954
Hi all. Have an issue i'd love some advice on if anyone would be so kind. Will try to be brief. Thank you!! So, have an intermittent RCD trip at...
Replies
43
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock