did an RCD test today on a cu and when I went to reset it the left hand RCD tripped. No tripping when circuits up an running just when I did the RCD test could anyone give me a heads up on what it could be thanks guys.
 
Not sure I've understood ... tested the RH RCD and it tripped as expected - then - reset RH RCD and LH RCD tripped immediately.
Is that it?
 
Possibly a high resistance neutral earth fault on the left hand RCD circuits. Remove the neutrals from the left hand neutral bar, left hand MCBS off and switch on the right hand RCD, mcbs on, and see if the high initial current trips the left hand one, reattach one at a time to narrow down.
 
Disconnect the neutrals and earths for the affected RCD and then it should reset. Reconnect until the offending circuit is found, im surprised you haven’t stubbled across this type of fault before.
 
To be fair it's something I almost never use. I'd use it as an ordinary clamp far more than as a mA clamp. I wouldn't really consider it an essential piece of equipment for most applications.

When diagnosing RCD tripping it's an important measurement to take ....
 

Reply to RCD shinaniginzzzzzz in the The Welcome Forum area at ElectriciansForums.net

Similar Threads

Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
767
I'm writing this mainly hoping something occurs to me while writing it! I got called to an occasionally tripping RCD. It's a Hager double height...
Replies
19
Views
2K
My circuit panel has two banks of breakers, each bank protected by an RCD. One of these RCDs has been problematic in that it trips intermitantly...
Replies
12
Views
1K
Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Replies
13
Views
1K
Hi, I swapped a 2 gang switched socket for a 2 gang switchless socket with usb ports downstairs. I switched off all the power to the house by...
Replies
8
Views
768

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock