can anybody help i did a rcd test on a circiut on a split load board and it triped out both sides of the board . I then tested a circuit on the oyher side of the board and that rcd did then not trip .I have checked for any neutrals on the wrong side but cant see anything obvious .never come across this before and wondered if anybody knows what would cause this
 
Its a new board just fitted and all new circuits in a house renovation I assume builders have fitted it and I was asked to test, all dead testing was fine 3 rings and 2 lighting all rings fine all r1 r2 fine all IR >299
 
disconnect all the circuits. then test RCDs. if they test OK trhen reconnect each circuit and test RCDs after each one. that'll trace the circuit that's causing the problem.
 
This sounds like a problem that I had a couple of years ago. I did the house rewire but it gets tested by the company spark (dont ask, he is a long story). Everything tested out great (as it should on a rewire) but when he put the cables back into the terms he did not mark them.......

He crossed over the incoming and out going legs to both RFC on both sides of the rcd's plus put a neutral in the wrong bar on one of the light circuits. What a rounded door handle.


Do a soft IR test on your L+N bars and see if something has been crossed over. Then look at each circuit one at a time (I'd start at the RFC) and identify each leg. The rest is just fault finding. good luck and give us an update with what youve found.
 
Is the db itself wired right? As in manufacturers connections?? Had one that wasn't recently.
Or is is a split load (16th)
So the two Rcd's are in series? Effectively.
Hope this helps.
 
Thanks for that suggestion sounds like I will have to get involved in other peoples work i just wondered if i was missing something simple as all looks ok in the board and all the other tests are fine all wiring looks fine
 
Yes checked all legs on rings and removed and reconnected all the circuits just to make sure that everything was in the correct neutral bar .The factory conections also look correct but they are in series
 
Its a new board just fitted and all new circuits in a house renovation I assume builders have fitted it and I was asked to test......

Oh dear, the builders did it. If i was you I'd ask for more moey now before you take all week to find out what they have done.
 
Yes checked all legs on rings and removed and reconnected all the circuits just to make sure that everything was in the correct neutral bar .The factory conections also look correct but they are in series

Are they both 30mA??
If one is feeding the other then it should be a S type for discrimination.
But then you wouldn't have additional protection for those circuits (if required)

Sounds like a typical builder install.......
'This board was cheaper!! I could just put a Rcd that side too'!!!!!
Lol
 
Had this on a rewire a year ago, later found one of the other sparks had wired the two way from the landing and hall wrong, 1mm's at bottom of the stairs with a feed and switch line, and a three core for the two way upstairs, the 1mm's for the hall light and the three core for landing light and switch fed it thinking it was a 1 gang switch not a 2 gang, could be a possibility
 
Yes really baffling me but fixed problem redid all tests and everything now spot on .but having said that builders are stil on site and loosening fittings to decorate and tile behind and such, so may have been something else as well .but i am paid now and everything was perfect when i left it
 

Reply to rcd test tripping both sides in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
315
Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Replies
13
Views
1K
Hi I am asking for help as a novice and 1st time user of this forum. Recently started to experience tripping of MCB & sometimes with the RCD at...
Replies
7
Views
529
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
778
Hi, I seem to have an RCD that keeps cutting the power at random times without actually tripping, if I reset it, the power comes on and will stay...
Replies
7
Views
443

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock