hello every one can some body help me please in this particular question?When tested at Idn time 5 , a 30nmA RCD protecting a 230 V a cooker circuit incorporating a socket outlet in its control unit must trip within : time please
 
Why does that matter?

afaik, the disconnection time for a TT system is 200mS @ x1, but can't find anything in the regs for a x5 time on a TT. perhaps that's driverman's concern.
 
The testing of a 30mA RCD at 5 x IDn is only applicable to an RCD providing additional protection to persons and livestock and the requirement in that case is for the RCD to trip in less than 40ms. This would be independent of the earthing system as the trip time is not related to the maximum disconnection times required for disconnection in the case of a fault.
 
Smilie
Bit of advice mate ask one of the mods for access to the trainee forum you will get more help, have you got a copy of the OSG? someone has mentioned this may be a homework question, the answer you are looking for, may be in the OSG page 105, you will get grief if you ask a question without researching it yourself, which in this case looks likely.
 

Reply to RCD test in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
315
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
Hi, I'm back in the electrical game after 9 years break so feeling a little rusty! I'm adding an additional socket to a circuit but the main RCD...
Replies
6
Views
1K
Bathroom with an electric shower wired to the latest regs with a 40A MCB and RCD protection. Is the disconnection time 0.4s or 5s. Looking at the...
Replies
15
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock