I am a relatively newly qualified electrician and have completed a re-wire but come across a problem i dont understand.

I have a dual board with a lighting and a power circuit on each side. On the right side the power and lighting is entirely stable, but whenever a load is applied to the sockets it trips the left side RCD.

When i put load on the left side power circuit or put on more then three LED lights it trips the left RCD.

I have tested all the cables and cannot find any cause (such as wrong wiring or nails through wires) for the tripping.

Any ideas please, please?
 
or 2 faults .......... one on each side.......

On a rewire its probably the easiest fault finding you can do .......you know where all the cables run, where all the points are .....
 
Probably something to do with the two way lighting circuit on the landing/hall lighting connections
 
I am a relatively newly qualified electrician and have completed a re-wire but come across a problem i dont understand.

I have a dual board with a lighting and a power circuit on each side. On the right side the power and lighting is entirely stable, but whenever a load is applied to the sockets it trips the left side RCD.

When i put load on the left side power circuit or put on more then three LED lights it trips the left RCD.

I have tested all the cables and cannot find any cause (such as wrong wiring or nails through wires) for the tripping.

Any ideas please, please?
Where are you in the UK
 
Either crossed neutrals in the board or two separate faults.

Crossed neutrals has caught me out before because I assumed BG had wired the DB properly...
 
Don't go wibble, and proceed in a logical manner, if need be go back to the beginning (testing). Keep thinking and take on the ideas the chaps have given. Think of it as a learning exercise. Something to store for the future. Every day is a learning day
 
Thanks everyone.

The part that i thought i had included but now realise i didnt is that everything was working fine until about 1030 on tuesday. The RCD tripped and i have done everything i can think of short of starting the board again.

The thought that it could be a 2-way switching problem is interesting and not one i had thought of. The are two 2-way switches - hallways up and down stairs - that are in 2g2w switches so maybe, just maybe the 2-way cables are 'crossed' and one of the other guys switched the switch.

Otherwise what would cause a borrowed neutral that just appears?
 
If you can track a working site back to a time when it did work, are you aware of anything that changed ? its been very wet around here so could water be the issue?

Done any DIY? Hung any pictures?

As for the 2 way switching, your dead tests should have shown this as an issue.
 
Sounds like an N-E fault on one of the circuits on the left RCD. Load on either circuit could cause it to trip. If your IR is good on both circuits, the fault could be within an appliance that has been plugged in to the left hand socket circuit - which might explain it having been OK at first.
 
Dead test results all good?

IR good in all switch positions?
 
A load on one half tripping the Rcd on the other half will have resulted from a interconnection between the 2 sides
With earth faults ruled out,it may be either the usual consumer unit cross over cock up or a external circuit cross over cock up

Because it didn't happen,then did happen,the chances are its a circuit cock up rather than a consumer unit cock up

The fault seems to me to have been switched into existence by actions,check those 2 ways again
 

Reply to RCD trip across board in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Replies
13
Views
1K
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
I have a client with what appears to be an intermitent fault on the lighting, but trips the power. The installation has a 16th edition board with...
Replies
17
Views
2K
Hi, I have run some outside lighting for a customer in Hi-tuff cable. He now wants 2 additional lights run across scaffolding which has been put...
Replies
13
Views
796
I have just checked a double outlet and it trips at 18ma. It was supposed to be faulty. Washing machine had a bad heater which got replaced but...
Replies
10
Views
553

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock