Hello All

A friend of mine has just had a CU change from an old re wireable fuse box to a new Dual RCD board i didnt do the job for him someone else did.

with the old board in place the immersion heater 3Kw worked now with the dual RCD board the immersion heater trips the main RCD the immersion heater runs though a timmer and is supplled by a 20A radial in a swiched fused spur with a 13A fuse

I thought this was to boarder line as 3Kw will pull 13A i would be looking to run off the radial a 20A DP switch.

Could it be that the 3 Kw element is slightly breaking down a is sensitive enough to trip the RCD.

Havent looked at the job just going by what ive been told.

Any thoughts

JS
 
Take the cover off the immersion heater where the cables are connected to the element. Many years of heating up does nothing positive for the insulation.

Had this exact issue this week when doing functional testing after a CU change.

13A FCU is normally OK for an immersion heater.
 
Usually one of two likely causes:
1) Poor termination of the the cable ends, usually the neutal connection leading to insulation burn-back. Remake the terminations after stripping back any conductor that has suffered. Crimp ring terminals to the neutral and cpc ends helps get tight connections.
2) IR test the element between line and cpc terminals, if <2M ohms replace element.
 
Last edited by a moderator:
99% it's the element. as markie says. IR the element.
 
ium going to say as Telex itrs the element they can be funny things if you get the slightest of moisture in the element then this can cause insulation failure what happens is the watter attacks the metal element causing very small holes in which dampness gets in although it would have worked with the 3036 rewireables , but with /RCD's they monitor for imbalances IE moisture between the cunductors within the insulation causing an imbalance , do an insulation test ,check element continuity then from one of the terminals of the heater to the earth connection and ill bet you its less than 2 meg ohms , dont remove it from the RCD thats the whole idiea of protecting the house with an RCD extra saftey find the fault and be safe !
 

Reply to RCD tripping immersion heater. in the Australia area at ElectriciansForums.net

Similar Threads

Hi all. Have an issue i'd love some advice on if anyone would be so kind. Will try to be brief. Thank you!! So, have an intermittent RCD trip at...
Replies
43
Views
3K
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
Hi, I know it's best practice to run an immersion on a dedicated circuit but am I OK with the following A new heat pump is being fitted and it...
Replies
7
Views
2K
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
Had a real headache of a fault finding job which has left me scratching my head - RCCB on a split load board, supplying 3 circuits (shower...
Replies
20
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock