Discuss RCD tripping when earth core touched in the UK Electrical Forum area at ElectriciansForums.net

K

Keefyjet

Hi,

As I understand, touching or cutting the earth core of a disconnected (via its MCB) circuit can cause an imbalance and an RCD trip – due to other working circuits connected to the same RCD bank.

So why doesn’t touching the earthed part of a working appliance (e.g. the chassis of a tumble dryer) cause the same imbalance and RCD trip?

Maybe I’m missing something blindingly obvious here – in which case please enlighten me.

Regards.


:21:
 
Are you sure it is earthed?

If your washing machine body is earthed and on a TN-C-S system the "Earth" and Neutral are effectively the same thing as they join together at the supply feed. You make a connection between your 'washers' CPC and the 'washers' neutral then it allows other circuits current an alternative path back (i.e. some current flows up the 'washers' neutral and down the 'washers' earth so passing the RCD and causing the inbalance).

There are a few assumptions there, the biggest being that you dont have a double pole 'washer' MCB and the neutral is isolated!
 
Not sure what you mean by touching the chassis of a tumble dryer? Touching with what? Your hand....?

Yes, as in providing another earth route, in this case via ones body. Why doesn't it unbalance the system in the same way as touching or cutting through the earth cable?
 
Disclaimer to this thread

Your understanding is appreciated
icon14.png

This new technology is only just a recent introduction to us in Wales
icon12.png
 
Touching an earth core shouldn't trip an rcd.
cutting the cables ( shorting the N & E) usually does

It depends what you touch the earth with, i'm confused aswell by the OP lol.

Stick your manhood on the earth, and you wont trip the RCD and if everythings in working order you won't get the thrill you're probably desiring.

Stick a line conductor on the earth, then you'll trip it.

Mr.Keefyjet what do you mean by touching the metallic frame of an appliance? I hope you're not suggesting, why should it not trip when you pick it up lol

I suggest reading up on earthing and bonding.
 
some good literature on that very subject by D .W. Cockbum, available from amazon. :carolers:
 
a pilot project in south wales introduced indoor toilets and bathrooms to a few select houses. when it was found that said toilets and bathrooms were being used to bath and shear the sheep, the project was abandoned in favour of underground housing, but those resourceful taffs kept coming back to the surface bringing up the coal.
 
Yes, the neutral is common but, as I understand it, the imbalance causing the RCD to trip occurs only if one or more of the other circuits under said RCD bank is/are in use? In other words if all of the circuits under the control of that RCD had no load the RCD wouldn't trip as there'd be no imbalance for it to detect?
 
I have to be honest and say this is the second thread that has had me confused

The earlier fuss about the bath in the bedroom
Our own baths in Wales would be in whatever room was the warmest
If it wasn't there,it would be on the nail in the yard
 
on the nail next to the vet's trousers when he was doing the artificial insemination bit to the cow.
 
Are you sure it is earthed?

If your washing machine body is earthed and on a TN-C-S system the "Earth" and Neutral are effectively the same thing as they join together at the supply feed. You make a connection between your 'washers' CPC and the 'washers' neutral then it allows other circuits current an alternative path back (i.e. some current flows up the 'washers' neutral and down the 'washers' earth so passing the RCD and causing the inbalance).

There are a few assumptions there, the biggest being that you dont have a double pole 'washer' MCB and the neutral is isolated!

Maybe i've misread the OP but i took it that it was 2 seperate unrelated questions...
 
the whole thread is unrelated now., it's well past beer o'clock and silly threads get sillier.
 
the whole thread is unrelated now., it's well past beer o'clock and silly threads get sillier.

It's past beer o'clock, but it's not quite reached the missus going to bed "i'll be up in a minute" quick look a babestation because we're mucky men thinking we were still 18 o'clock.

HAHHA

Thats not me btw(honest sir), just my impression of what Geordiesparks like come bed time LOL.
 

Reply to RCD tripping when earth core touched in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

My circuit panel has two banks of breakers, each bank protected by an RCD. One of these RCDs has been problematic in that it trips intermitantly...
Replies
12
Views
1K
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
1K
I'm in a questions asking mood tonight. I briefely looked at a job today and I need to recommend a board change but need to justify it. Firstly...
Replies
7
Views
1K
Afternoon all, I have an issue with the loft socket. When we moved the previous owners had a 2.5mm cable going up from the CU Via FCU however...
Replies
7
Views
1K
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock