keithbr13

Hi Every one, I have been asked to look at a problem in a toilet when the light is turned off the RCD trips intermitenetly but not when it is turned on. There is a fan and small flourescent shaver light in the room . the instalation was rewired by me about 10 months ago all the test results were as you would expect.
 
Well have to admit that is a first for me ......turning something off and it trips.

There as to be some sort of in balance here or a dodgy RCD. Have you ramped tested the RCD? What is the protective conductor currents on the RCD circuit(s)?

Just a start
 
A stab in the dark...
Could the act of switching off the shaver flu be causing a high voltage back emf in the choke/transformer which is breaking down the insulation in it's coil winding, or possibly some other point of weakness in the insulation of the circuit?
 
Seems odd .

Have they left the light switched on for long periods to come to that conclusion.

If not the RCD at fault it may be your looking in the wrong place.


Try clamping the tails with the light on then switch it off to see what the leakage is !
 
A stab in the dark...
Could the act of switching off the shaver flu be causing a high voltage back emf in the choke/transformer which is breaking down the insulation in it's coil winding, or possibly some other point of weakness in the insulation of the circuit?

they mention that specifically in the 'rcd handbook december 2010'
as a source of these transient overvoltages
-switching off fluorescents with no pfc cap in them

dont know if that's the issue here

another poster suggested a snubber across swich contacts for the arc
also ABB make an anti-nuisance trip rcd if no faults show up in regular testing
 
Be careful here! Although a snubber might quell the switching transients and prevent the RCD from tripping in the short term, it's only the 'tip of iceberg'.
The under lying problem here is one of high standing leakage on one or more of the final circuits attached to that RCD, the switching transients in the toilet just push the RCD over the tripping threshold, but can't possibly be large enough in this case to cause the tripping alone, as a large reactive load or resonance would be required. Focus your attention on finding and reducing the high standing leakage current. Then the need for a snubber will become unnecessary.
 
Be careful here! Although a snubber might quell the switching transients and prevent the RCD from tripping in the short term, it's only the 'tip of iceberg'.
The under lying problem here is one of high standing leakage on one or more of the final circuits attached to that RCD, the switching transients in the toilet just push the RCD over the tripping threshold, but can't possibly be large enoughag in this case to cause the tripping alone, as a large reactive load or resonance would be required. Focus your attention on finding and reducing the high standing leakage current. Then the need for a snubber will
become unnecessary.
agree he should test first
i can see how standing leakage might be the underlying issue
in the rcd handbook they say the issue is overvoltage transient+capacitance to earth from wiring and equipment
 
Last edited by a moderator:
Hi All thanks for the answers, can I just ask what a snubber is ? which book are you refering to ? how would you go about testing the other circuits attched to the RCD
Thanks again
 
Hi All thanks for the answers, can I just ask what a snubber is ? which book are you refering to ? how would you go about testing the other circuits attched to the RCD
Thanks again

Do you have a earth leakage clamp meter ?

Disconnect all loads from the RCD and ramp it to find out when it is tripping. (mA)

With your clamp meter on the tails switch on the loads one at a time to find out which if any is excessive.

I take it that all your IR tests for the ccts are good ?

Its very easy to look in the wrong place with RCD faults when they are protecting multiple mcb's!

Have a look at Markies post on this thread re a snubber!
Flashing Light bulb when switchs are off...
 

Reply to RCD Tripping in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
290
Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
Replies
19
Views
1K
Hi, I swapped a 2 gang switched socket for a 2 gang switchless socket with usb ports downstairs. I switched off all the power to the house by...
Replies
8
Views
758
Hi all, we had our gas hob removed months ago and finally just got round to putting an induction hob in. Its a normal 4 ring induction but one of...
Replies
3
Views
762

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock