dlt27
-
- Reaction score
- 26
Can anybody help... Went to a job Friday where apparently RCD is coming out once every couple of nights. The rcd covers 4 circuits which are sockets, sockets, heating and outdoor shed. I have carried out a blanket test and I am getting a reading of about 20M This is with loads conncted apart from 2 neon extension leads which if connected brings it down to 0.39M.(still to high to cause tripping). I have also done a ramp test on rcd and it comes out at 23mA. Finally put clamp meter around tails serving rcd and with loads connected was still only getting 10.5mA of earth leakage. Thanks for any advice.