Discuss RCD won’t trip help needed in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
51
TT system, have upfront 60947-2 with added on 61008 with mA and ms settings, now I’m getting Zdb of 22.9 ohms and Ka of 4.0, now the RCD can be what ever I set it to but I’m struggling, I’ve set it to 300ma and 300ms but can’t seem to get it to trip? I also have a split phase supply so have L1 and L3 and N but can’t trip on either phase thanks
 
Long shot but have you tried the manual trip on the RCD. I have found a few times that because no one has ever tested with the manual button the RCD sticks and you have to switch it off and on before the manual works let alone test current on the circuit.
Yes mate, all ok the RCD I have has a green LED light to show RCD function is on, thanks anyway and it’s brand new
 
I have another lad coming tomorrow with a different tester and I have a Martindale ET4000 and yes tester will not give a reading above 300ms flashes red but surely the RCD should trip within 300ms x1 to comply?
 
That’s an additional 300mS to the tripping time the RCD normally has.
 

Reply to RCD won’t trip help needed in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Evening all, I have a little conundrum I need to get resolved. I’ve moved an EV charger from a single phase board that was on a 40a breaker and...
Replies
9
Views
544
I need your help please once again in tracing a fault. Am DIY but not clueless. Converting former kitchen into 2 rooms: bathroom and laundry. The...
Replies
24
Views
2K
Hi all, So I’ve been having a strange fault in my house which has just appeared over the past few days. About a month ago I moved my pc set up...
Replies
136
Views
14K
Hello all I have recently installed a sub main in 4mm 3-core SWA, approx length 45 metres, to feed a small garden office. Final circuits in the...
Replies
7
Views
2K
Hey all, I’m an electricians mate, trying to get fully qualified but struggling. I’ve got my L3 diploma (C&G 8202-30) and 18th edition, I have...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock