Commercial greenhouse - panel has a 4 pole 40A 300mA rcd feeding 3 x 3phase 16A socket outlets with 25A 30mA rcd's built in. Under 17th edition is this 300mA illegal. Customer wants local RCD's for ease of nuisance trips.
 
What makes you think it might be 'illegal' ?

Without more information, it's hard to say if the 300mA rcd is required and if it is then the chances are unless it is a time-delayed 'Selective' type, you'll still end up with 2 devices tripping on a fault.
 
illegal (wrong word) special locations agricutral less than 20A fit 30mA rcd. Panel rcd protecting all cable going out onto metal structure etc. But customer wants exsisting sockets left with local RCD's. get my dillema ?
 
All circuits must be RCD protected in Agricultural premises.
Circuits that supply socket-outlets not exceeding 32A require up to 30mA.
Those that supply socket-outlets that exceed 32A require up to 100mA.
All other circuits, lighting distribution etc. require up to 300mA.
This information is contained in Section 705 of BS7671.
You can use lower rated RCDs than the maximum specified in BS7671, but that won't help stop nuisance tripping.
Do better finding and rectifying the fault that is causing the nuisance tripping.
 

Reply to Rcd in the Canada area at ElectriciansForums.net

Similar Threads

Did a couple of inspections on 2 x 2 bed ground floor flood damaged flats today, only 4 circuits in each, bizarrely one socket circuit and 2...
Replies
6
Views
2K
Afternoon all, Got a bit of a strange one (by my usual standards anyway). Job is a large barn conversion, done years ago, there's loads of work to...
Replies
6
Views
1K
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
1K
Hi all, Great to of found this forum. Much respect for keeping everyone safe! My background is in commercial data and Audio Visual. Been...
Replies
0
Views
497
Hi friendly people, As you may be aware, I'm a plumber, so quite possibly what I am seeing is correct, though it seems a bit odd to my untrained...
Replies
4
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock