Discuss RCDs in a tt system in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

B

big willie

I recently installed a split board wylex consumer unit in a tt system that had been converted from a tns system by the provider about three years ago.The old system consisted of a consumer unit with old mini breakers only.When the system was changed to a tt the provider installed a 100Ma rcd external to the consumer unit as an on and off switch. Now that I have installed a new fully compliant with the 17 edition fuse board protected by two 30Ma rcds do I still need the 100Ma external RCD. EFL at source is 19.7 OHMS.
 
It's not doing any harm and a back up in case one of the RCDs fail.

It can also be used as an isolator for the new cu.

Why was the system changed from tns to tt?
 
I recently installed a split board wylex consumer unit in a tt system that had been converted from a tns system by the provider about three years ago.The old system consisted of a consumer unit with old mini breakers only.When the system was changed to a tt the provider installed a 100Ma rcd external to the consumer unit as an on and off switch. Now that I have installed a new fully compliant with the 17 edition fuse board protected by two 30Ma rcds do I still need the 100Ma external RCD. EFL at source is 19.7 OHMS.

No. .
 
I recently installed a split board wylex consumer unit in a tt system that had been converted from a tns system by the provider about three years ago.The old system consisted of a consumer unit with old mini breakers only.When the system was changed to a tt the provider installed a 100Ma rcd external to the consumer unit as an on and off switch. Now that I have installed a new fully compliant with the 17 edition fuse board protected by two 30Ma rcds do I still need the 100Ma external RCD. EFL at source is 19.7 OHMS.


They wouldn't of got away with that little move if it had been my installation. Fine if it was a temporary measure, but no way as a permanent bodge job!! They are duty bound to ''maintain'' a previously DNO provided TN earthing provision!!

As for your query, it would be prudent to change that straight 100mA RCD for an S type 100/300mA RCD. Why, because you're totally relying on a single RCD (either side of the split CU) for your earth fault protection, on a TT system without it. And unfortunately RCD's are just not that reliable to be trusted, especially over extended periods of time. As others here have stated, it will also provide a useful means of isolation to the main CU.
 
Last edited by a moderator:
I think it was because the sweated earth connection to the incoming main had become detached and they could not get the EFL low enough with a strap on. And further more some dno's dont allow strap ons anymore
 
I think it was because the sweated earth connection to the incoming main had become detached and they could not get the EFL low enough with a strap on. And further more some dno's dont allow strap ons anymore

Of course they do, what they don't, or shouldn't allow is BS 956 clamps to be attached to PILC cables. But Hepworth and constant force spring clamps are pretty much in standard use by all DNO's for upgrading or reattaching main earthing conductor sizes to PILC cables...
 
I think it was because the sweated earth connection to the incoming main had become detached and they could not get the EFL low enough with a strap on. And further more some dno's dont allow strap ons anymore

surely, someone called 'big willie' would never have to bother with a strap-on.
 

Reply to RCDs in a tt system in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Replies
18
Views
2K
Keeping this brief.....................New dwelling.....TT system with 100mA S type rcd protected supply to local board with 30mA RCD. Freelance...
Replies
21
Views
3K
Hi Guys, hopefully someone will know the answer. Testing an install on a (domestic) PME system I have a garage consumer unit supplied from one of...
Replies
17
Views
2K
Hi Guys, Long time member and not a regular user here. I do pop in here when the odd unknown pop's up and unable to locate an electrical dilemma...
Replies
4
Views
853

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock