My question would be, say if you're PFC and PSSC are less then 18,000 Amps, why would you use a MCCB over an MCB on a main DB supplying a sub DB?
 
Your tripping characteristics are completely different from your standard circuit breakers hence manufacturers data should be sought as have you never noticed how no maximum zs values are published in bs7671 regarding mccb’s?
They can have both the magnetic and overload characteristics set , depending on the application they are being used for and what they intended to supply and protect.
 
Okay Gigsy, from afar and not seeing the job first hand this is probably what I would do. Shorten the swa supply cable and make it off into a 63A isolator, from here take some 6181Y tails to the meter that way you have no unenclosed conductors. Those protective devices at the main board with the orange toggles are BS3871 Type 3, cant make out the other but it is not compatible with the enclosure and the cover has probably been cut away to fit it.
 
Okay Gigsy, from afar and not seeing the job first hand this is probably what I would do. Shorten the swa supply cable and make it off into a 63A isolator, from here take some 6181Y tails to the meter that way you have no unenclosed conductors. Those protective devices at the main board with the orange toggles are BS3871 Type 3, cant make out the other but it is not compatible with the enclosure and the cover has probably been cut away to fit it.
Thank you :)
I will not use rear entry again. From now on 4 inch metal trunking top and bottom into glands and make off the SWA into the board. And I would insist on the customer purchasing the meter designed to go in the board.
 

Reply to Rear entry three phase board in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi guys, So, a friend of mine has a three phase 100a supply and wants to install 2 x three phase 20a fork lift chargers and a three phase car...
Replies
24
Views
3K
I have a scenario where there is a three phase DB in a commercial property where there are mixture of three phase and single phase washing...
Replies
2
Views
816
Hi everyone, this ones a first for me but weve been asked install and use a three phase supply in a large new build house. The 16 way dis board is...
Replies
5
Views
2K
Hello, I'm new to this forum, we are in the process of converting into 12 flats all electric, no gas incl. heating, showers etc. An electrician...
Replies
10
Views
2K
Hi Looking at a job currently adding a 3 phase solar installation but the distribution board is full obviously a new board is the best option but...
Replies
9
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock