Discuss Recognising a duff panel in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

P

pjcomp

Theory's great but it's only when a problem comes up you really start to learn things..... My relatively low number of installs to date have gone to plan so I'm hoping a few of you out there have hit more problems than me.

Just put up a 14-module rooftop, two strings of 7x245W panels. Al lthe panels checked OK on the ground. When it came time to connect up, one string gives me 242V, the other one 172V. The arithmetic says I've got two duff panels in the second array.

Questions: Am I missing a bit or does it indeed indicate two duff panels? If they tested OK on the ground, what should I be looking for in retest (I'd prefer to have a few ideas before I start pulling the array apart)? All suggestions gratefully received.

PJ
 
Thanks Biggs - had an issue with this manufacturer a few months ago when all their panels were wired back to front (male plug for neg, female for pos) so this might have slipped through again somehow. Got any suggestions for pinpointing which one it might be?

PJ
 
It depends how easy the plugs are to get to. I'd disconnect the array so I had both ends at the array. I'd plug a fly lead into one of the ends and go down the line checking the voltage. What make of panel are they?
 
OK, update, big thanks to Biggsy, and one worth noting to anyone else reading this.

It was indeed a panel with revers polarity - or to be more precisse, six panels with reverse polarity.

Of the 14 panels delivered, six had a different version of MC4 connectors; not the end of the world to swap a couple with standard ones to connect up. What eventually transpired, however, after a lot of to-ing and fro-ing with the suppliers, turns out these six were wired back to fornt, ie the male connectors were neg and the female were pos. thus the one in the 7-string that was the "correct" way round was the one with, efectively, reversed polarity. So, a bit of panel juggling on the roof and plug changing, and a properly working array. Phew.

Another one to clock up to experience.

PJ
 
good thread, what make of panel, i will teach the apprentice the finer points of polarity checking on every panel not just the basics

thanks
 
To be honest, I never check polarity with the panels. I test that I get a feasible voltage and Isc and that's it. I will definitely keep my eye on polarity from now on though - not that you should have to. Panels aren't cheap and I'd be interested to know which manufacturer are throwing out these shoddy modules.
 
The panels were DelSolar, made by Delta, perhaps more relevant the reversed connectors were by Tyco. It's not the first time I've been bumped with "non-standard" MC4s so that alone didn't set off alarm bells

PJ
 
Last edited by a moderator:
Biggs when I did the Ecoskies course they made us go out and do the panel tests VOC Isc etc, all Ok. Then we were brought back inside and did some more work and then split into groups to do a string.

The guy brought out several panels for us to wire and we started, 2 of us testing and 2 stringing. luckily I was testing and one panel showed the -(minus) on the Dc range so I dished it. Any way he came out and asked ok, and we told him yes gave him all the reading of each panel and then the string, and he asked did we have a problem, I said yes one panel had reversed polarity, and he was so ****ed that we found it as it was his little test !!!!
 

Reply to Recognising a duff panel in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

At work we've got an 8 panel single string set up, going into a 3000w inverter via a double pole DC isolator. The AC goes supply > isolator >...
Replies
11
Views
3K
Hello all, I've just been perusing the AM2/E/S threads on here. Thought you might like a bit of a review. If, like I did, you find yourself...
Replies
7
Views
2K
Hi everyone, I have a quick question if I may? I'm thinking of adding a second PV system to my existing rooftop PV & battery setup. As the...
Replies
0
Views
1K
Hi guys, I am new to the forum so be nice! I used to install solar PV systems back when the tariffs were still good, and I've never had to go...
Replies
5
Views
5K
Hi I don’t know how resolve this so any helpful advice would be greatly appreciated. I have no electrical knowledge. I will try to be as clear...
Replies
57
Views
11K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock