Jimmyb

hello, What ref method would you class this cable there will be 100mm of king span to put in but the cable will be above the king span by 10mm or more so not in contact with any insulation.

thanks

Refence method, disagree meant on a job 29102010968 - EletriciansForums.net
 
101, clipped direct with no insulation above.
 
sorry 101 is insuylation not exceeding 100mm. 100 is what i shouls have said for no insulation above
 
just got on site guide out and 101 is insulation exceeding 100mm, 100 is insulation not exceeding 100mm, and c is clipped direct.

are u saying it's clipped direct or insulation not exceeding 100mm

thanks
 
Clipped direct if not touching,10mm enough for heat to dissipate. What circuit is it for?
 
kitchen (extension) radial, builder's sparky reckon it method 100 so will have to be made in ring which is sort of problem cos bathroom floor has been tiled now so hard (impossible) to get a another cable though but could use shed cable as its also 4mm and run new cable outside for shed but i was sure its classed as clipped direct and didnt want a cable on outside of building if possible.
 
because 4mm with ref 100 only takes 27amp and wouldnt want a kitchen on any less than 32amp
 
just woke up. re-read post correctly. cable is not covered by any insulation, so therefore its method C , clipped direct.
 
farm job yesterday, all ladder work and dodging fork-lift trucks driven by farmers. fell asleep after 3rd pint
 

Reply to Refence method, disagree meant on a job in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock