Discuss Replacement Distribution Boards in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Reaction score
34
We are down to replace various DB's on old type commercial buildings, having looked at the install, they are in a bad state of repair, does the replacement DB, require RCBO's for all lighting circuits due to the cabling concealed in walls etc. Or can you fit like for like as it's pre 17th or is it up to the client discretion?
 
Your work as to be done to the 17th regardless of what edition the existing installation is in.

As this is a commercial installation I'm sure you can evoke regulation 622.6.7 for under the supervision of skilled or instructed persons for the cables.

As for other areas such as socket outlet not exceeding 20amps you would really need to assess each circuit,for example if they could be used for mobile equipment outside then you need to RCD them, but others can also come under 411.3.3 and the same skilled or instructed person.
 

Reply to Replacement Distribution Boards in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

As a retired electrician, I need to specify a new type B board for a village church. Principal load is heating. Ipfc phase to phase is 1.1kA...
Replies
10
Views
1K
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
Morning guys, I would like some advice, currently at my workplace, I am replacing a DB and existing wiring in a warehouse. One of the ways feeds...
Replies
4
Views
1K
Hi all, a very long time I did a swanky grand designs type new build in the middle of nowhere, so in the middle of nowhere that it's a house with...
Replies
1
Views
260
Helloo guys, First post, so sorry if this is dreary! I'll try keep it simple... I have a client with a distribution circuit supplying AC...
Replies
4
Views
889

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock