I was changing a consumer unit today and the DNO's main cut-out was a porcelain rewireable fuse inside a hinged metal unit. There were no markings on the fuse-holder, and the fuse consisted of two strands of wire, approx 0.75mm dia each.

I'm afraid I haven't seen one like this before. Can anyone tell me how I can work out the rating of this fuse? And what I should note it down as on the cert?

Thanks.
 
well for a start i would normally just sit back and observe fuse pulling on DNO aperatus.....but these old cutouts with ceramic type rewireable fuses can be dangerous....as they can just drop apart in your hands....so all`s you end up with is a fistful of copper....
you should avoid pulling them...but if you must then always, always use insulated pliers/grips to do it...just in case...and never under load...
as far as these old cast iron cutouts are concerned...the DNO are in the process of replacing these....
so give them a bell...get on to the duty engineer....they should send out relevent paperwork for the client to fill in and return as regarding the replacement of this for a new one....
 
yep. get DNO to replace free. this should have been done 2 years ago, but as there is no money in it for DNO they're dragging their heels waiting for us poor sods to do half their dirty work.
 

Reply to Rewireable main fuse. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, I am looking for some advice regarding old rewireable (3036) fuse boards in regards to additions and alterations. I am an electrician and...
Replies
28
Views
4K
I'm having an extension built and the builder leading the project has said that the electrician will be over in about 4-6 weeks to start his works...
Replies
4
Views
2K
Hi all, I have been on a site repairing damage caused by travellers collecting copper for the last week. We have found and replaced cabling to get...
Replies
17
Views
3K
Hi all. I have a question i'm hoping some of you can advise on. A long story short my main fuse has been hidden in the wall cavity(by the previous...
Replies
21
Views
2K
About 15 years ago, after having had a modern consumer unit fitted, and prompted by our electrician, I asked my then energy supplier (Tonik) if...
Replies
25
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock