Discuss RFC LN-E IR 0.15 ohm - why was the RCD not tripping? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

S P

-
Reaction score
21
Small job adding a few sockets, while doing some preliminary checks I found this reading on the socket circuit! :eek::(

After hours of fault finding -
Searching for any possible connected loads -
Questioning if the SFS's were DP then disconnecting the load N (found SP SPS's online) -
Breaking circuit in halves each time left me between 3 sockets....

The one in the middle was a radial! :mad:
Lifting floorboards searching for a JB, the spur from the middle socket disappeared into a bedroom towards under a large wardrobe! :eek:
(FFS, quick smoke)

Sticking my head and torch into the floor voids tracing the leg from the previous socket I noticed the cables appeared to go down to GF.
Found a socket behind a radiator!
Above that was a picture..., tested from nearby socket to picture hook SAME READING!
Removed picture hook and reading dramatically improved :D

It was already very late and I still had to put back all I'd taken apart so will chop the wall section tomorrow to repair.
Client was very happy the problem had been found but I couldn't explain why It hadn't caused the RCD to trip??

BTW - RCD test have been carried out and all ok.
 
Was the 0.15 continuity or IR? My testers IR resolution would never go down as far as 0.15 ohms, so am wandering if you meant Megohms?
And if it was Megohms, then thats still way above what it would take to trip a 30mA RCD. It's late and am tired but think around 7000 ohms is the region in which a 30mA will trip.
Good find by the way, sounds like you had fun in the process!!
 
This type of fault will not necessarily trip an rcd if the current decides to be more biased toward the neutral path thus not creating a sufficient imbalance to trip the device.
 
basics. ohm's law. for a 30mA RCD, R=V/I, so R = 230/0.03 = 7,667 ohms. ssssimplesss.

in the real world it's 240V so R = 8k ohms. theroretically, but will be a bit more, as most RCDs trip around 23 -25mA.
 

Reply to RFC LN-E IR 0.15 ohm - why was the RCD not tripping? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Dear Forum, I am hoping you can help as not only have I already had a qualified electrician out who couldn't find the problem, I've put in hours...
Replies
9
Views
6K
Customer has rcd which keeps tripping in no pattern. Split load board 16th type rcd on sockets cooker shower. Ze and as good, Ir test shows all...
Replies
16
Views
5K
Hi all, wondering if anyone can help me with a recent issue I've had with electric UFH in a small flat. Found that when the UFH starts, the RCD...
Replies
19
Views
16K
I have a very strange repeated RCD tripping scenario, which appears to suggest that two unrelated circuits are connected. Any problem solving...
Replies
87
Views
12K
Hi all. First time poster here with a hell of a lot less hair than I had 3 weeks ago now! so please be nice, I'll try and explain best I can. I...
Replies
44
Views
15K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock