Discuss Ring Circuit Question in the UK Electrical Forum area at ElectriciansForums.net

D

dancematic66

Hi all,

In my house I have a ring main which covers two floors, from which I have created two spurs with 2.5mm cable.

I am drawing 3000W on each spur and on the ring sockets probably around 500w making a total of 6500w.

Do you think this is dangerous as it is exceeding the 24A rating on 2.5mm cable which the circuit is wired with or is it ok as the ring circuit will allow larger current's than the cable rating states (In theory)?

Thanks for your help!

If I haven't explained my query in great enough detail please let me know and I will elaborate further.
 
as long as each unfused spur is 13A, then that's OK. dont forget that the current drawn by the 2 spurs is shared by the 2 legs of the ring. only problem would be if the spurs were near to 1 end of the ring, tham the current through the short leg would be greater than that in the longer leg.
 
Hi telectrix,

Thanks for the reply.

The two spurs are running a max current of 13A however I can't determine at which point of the ring that spurs are connected and now I'm worried about your last comment.. :-/
 
Basically, the load on a ring needs to be reasonably distributed to avoid overloading one leg, so you wouldn't want 26 amps being pulled at one end of a ring.

You don't say what the spurs are supplying, if they are fixed appliances at 3kw (like heaters) then they should have had their own circuits installed, back to the consumer unit, on 16 amp circuit breakers.
 

Reply to Ring Circuit Question in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi guys, newbie posting! Does the following sound ok... Existing circuit: SOCKET on a ring -> spur to SWITCHED 3A FCU -> SWITCH -> hardwired FAN...
Replies
11
Views
657
Hi everyone, I've got an electrical ring circuit that looks somewhat like the drawing below, where the blue sockets are part of the main ring and...
Replies
2
Views
1K
Essentially I have a "normal" socket in a ring mains, i.e. one 2.5mm T&E going in and one 2.5mm T&E going out. I am looking to simply add two more...
Replies
2
Views
278
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Evening all, Been to a job on Fri where the customer had a condition report completed. Two of the remedial identified was that there were too...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock