Hi All,

Will post an introduction on the new members forum but need to blurt out my question while its still in my head.

Me and Mrs JimmyB1988 have moved into our first house, it has a split consumer unit, half on RCD half not, my sockets were on the half without an RCD. One breaker does all the sockets including the Kitchen. So I moved the sockets breaker over to the RCD side, moved the neutrals too over to the RCD neutral bar. But it keeps tripping the RCD, all works fine on non protected side, i insulation resistance tested the circuit and reads 0Mohms between line + neutral, neutral + earth, line + earth? Confused?
icon9.png


Can anyone think of anything obvious?

Thanks Guys/Girls
icon7.png
 
Sorry can you just clarify the readings as not 100% sure about what you have written.

Line to Neutral =
Line to Earth =
Neutral to earth =

Also can you provide

r1 =
rn=
r2 =
 
Hi,
Firstly I see your qualifications are in Engineering, although you may have electrical experience.
You need to double check the cables you have moved across are definitely the Line Neutral & EARTH for that circuit.
Secondly , unplug everything from the Ring Main to check whether it may be an appliance fault.
Finally, If you are using an IR tester it may show a dead short, but can be higher due to the resolution of the meter.

This should get you started anyway.

Regards.
 
Hi,

Line - Neutral 0.00 Mohms
Line - Earth 0.00 Mohms
Neutral - Earth 0.00 Mohms

I have unplugged everything in every room, and the boiler is on a spur from the ring which i've knocked off. Cooker is on the ring, but i knocked that off too. (As I type I realize the extractor is on the ring too so i will try again with that disconnected)

I switched off the main switch at the c/u, I disconnected the ends of the ring from the breaker and neutral and earth bar.

R1+R2 is 0.32 ohms
 
Them IR readings are a dead short, looks like someone had a fault and changed it non RCD protected to stop it tripping, or you haven't actually disconnected the cables from the DB.
 
Yep I'm a maintenance guy, so i have a bit of knowledge about electrics and access to meters etc from work. But i'm no domestic electrician.
 
Yep I'm a maintenance guy, so i have a bit of knowledge about electrics and access to meters etc from work. But i'm no domestic electrician.
Why do people write this? the theory and practice of electrics doesn't differ much between commercial and domestic, especially when it comes to this stuff!
 
When you did the IR test what test voltage did you have your tester set to? If there's still something connected such as an electronic ballast or TV amplifier if might give you low IR readings due the test voltage exceeding the clamping voltage of the built-in surge arrestors.
 
The opening post had good concise info and there's obviously a good degree of competence so I've left the thread in the General forum.
 

Reply to Ring Main Tripping RCD, Line to Earth reads 0 in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi guys. Having a weird problem in a house that has suddenly happened. One half of the ring main has 240ish volts (fluctuates of course), and...
Replies
9
Views
465
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
734
Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
Replies
19
Views
1K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi Guys, Long time member and not a regular user here. I do pop in here when the odd unknown pop's up and unable to locate an electrical dilemma...
Replies
4
Views
835

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock