ring main

Discussion in 'Electrical Forum' started by trickyb, Feb 25, 2012.

Discuss ring main in the Electrical Forum area at ElectrciansForums.co.uk.

Thread Status:
Not open for further replies.
Please make sure you checkout our forum sponsors, many do discounts for members and, they keep the forum free to use.
  1. trickyb
    Offline

    trickyb Guest

    OK all heres the scenario fitting new cu in a house its on old 3036 type no rcds in sight . anyway testing reveles no ring curcuit one 2.5 supplys all sockets the other 2.5 in the same fuse holder supplys one socket upstairs in corner bedroom ? took socket off has 2 live & 2 neutral black/red wires ? propity has been extended at back and side . not been in this trade long but is it common practice to put a ring upstairs and spur downstairs ? because all groundfloor sockets look like spurs. :smile5:
     
  2. i=p/u
    Offline

    i=p/u Electrician's Arms

    vew pics, might help somone awnser,, very hard to give an awnser
     
  3. Murdoch
    Offline

    Murdoch Regular EF Member

    Location:
    Woking
    Did a CU change on a house like this lately - had ring circuit but all sockets have 1 wire - 1970 ish (must be loads of hidden JB's)
     
    • Like Like x 1
    Last edited: Feb 25, 2012
  4. spark 68
    Offline

    spark 68 Electrician's Arms

    Location:
    UK
    I have seen on older properties, a front-back split (division) of circuits, rather than the more usual upstairs downstairs, and on occasion where there has been a full height extension added, a side to side split.

    I think this was done prior to the advent of the splitload CU, so that you could still have power and lighting on each floor, if a fuse blew, some of the more senior members may care to elaborate
     
  5. spinlondon
    Online

    spinlondon Forum Mentor

    Location:
    Harlow Essex
    What rating is the fuse?
    Sounds like it should be 20A.
     
  6. Guitarist
    Offline

    Guitarist Electrician's Arms

    Location:
    Norfolk
    During the 70's many builders installed a ring main upstairs then dropped spurs to each downstairs socket to save money on cabling.....
     
    • Like Like x 2
  7. Guitarist
    Offline

    Guitarist Electrician's Arms

    Location:
    Norfolk
    Was considered adequate at the time as most households owned about 6 things needing a mains supply :cheesy:
     
    • Like Like x 1
  8. trickyb
    Offline

    trickyb Guest

    Hi had a 32A fuse in the ring curcuit or should i say what it supposed to be a ring! don,t think it,s all radials not with 9 sockets on one wire and 1 on another!should i try to join ring?
     
  9. brucelee
    Offline

    brucelee Electrician's Arms

    Location:
    leigh,lancashire
    same as my brothers a ring hidden under floorboards WITH LEGS TO DOWNSTAIRS SOCKETS the upstairs are wired as normal they must have done it to save on cable lol
    and that the best of the wiring
     
  10. trickyb
    Offline

    trickyb Guest

    so what your trying to tell me is this house is full of JB,s ! lol
     
  11. brucelee
    Offline

    brucelee Electrician's Arms

    Location:
    leigh,lancashire
    possibly mate
    at the board you have 2 legs upon testing you revealed one radial had one socket did you say though that this had two individual T/E if so were does the other cable go ?
    and the other 9 do they all have 2 legs or has one got 1 leg
    If so then maybe at some point someone has disconnected the ring and made it 2 radials maybe due to fault but then didnt replace the fuse with A SMALLER RATING AS SPIN SAYS 20A or they were doing a little DIY
    or try to locate the break if there is one it could just be it was wired as a radial with 9 sockets then someone ran another seperate radial to supply the individual skt

    so on testing you had no end to end reading on the Lines, neutrals and cpcs

    try testing from ccu to first socket and so on to find the last of the 9 skts if this has 2 CABLES WERE DOES THE OTHER GO

    in my brothers house its the same as i described above
    then there is also a seperate radial circuit to a JB its looks like 4mm but is stranded imperial then from the JB there are 3 seperate 2.5mm equivalent imperial twins supplying 2 sockets in living room and 1 in the hall
    then the other circuit is a ring circuit under floor with a single drops to sockets in living room and hall
    half the kitchen is wired to this ring then the newer part which is a extension into the old attached garage has a newer ring installed from a seperate ccu
    this will be my next project and it would be easier to rewire but not possible
    all upstairs have the correct wiring well of a fashion
     
  12. Guitarist
    Offline

    Guitarist Electrician's Arms

    Location:
    Norfolk
    The spurs were often straight out of the backs of the upstairs sockets so may not be many jb's at all.
     
    • Like Like x 1
  13. Rockingit
    Offline

    Rockingit Forum Mentor

    Location:
    Somerset
    Well I guess that even now in 17th, there's nothing technically wrong in wiring one circuit (be it ring or radial) upstairs and dropping spurs from each point to run down, it's just not that clever an idea, really, and makes it a real sod for the next sparks in the place to diagnose a fault!!
     
  14. rich.250
    Offline

    rich.250 Electrician's Arms

    Location:
    Cornwall
    Business Name:
    Rich Williams Electrical
    A 2.5 to a jb then spider off to everything seems to be common in older places. On a 30a,
    Needs to be down rated as spin and a few said to 20a max.

    Just cos the socket has two cables in the back doesn't mean it's a ring necessarily......
     
    • Like Like x 1
  15. rich.250
    Offline

    rich.250 Electrician's Arms

    Location:
    Cornwall
    Business Name:
    Rich Williams Electrical
    Do people have to use the term ring main.....
    You could try and put a socket on a ring main. Be a good watch.
    Maybe I'm grumpy this morn.
    Sorry guys
     
    • Like Like x 2
Loading...
Similar Threads - ring main Forum Date
OK to spur lights from ring main? Electrical Wiring, Theories and Regulations Feb 9, 2019
Trainee Single Pole Fused Spur From Ring Main Electrical Forum Feb 9, 2019
Thread Status:
Not open for further replies.

Share This Page

Electricians Directory Post a Domestic Job Post a Commercial Job